    Cant get Ra <200ohms

    Ring the local supply company , I've come across unrodded tranformers , or nicked rods and cables at the suppliers transformers . Especially on transformers mounted on poles . But sometimes it's just down to the location. As long as it complies with bs 7671 and the touch voltage rule then there...
  2. H

    fault finding

    AM2 , acheivement measurement 2. Under city and guilds , apprentices sit 2 AM tests . An AM1 and AM2 , an AM1 is usually sat after the first year and is used to check basic circuit knowledge and clipping t+e , bending radii etc . AM2 involves a complete installation within a set timeframe ...
  3. H

    Zs live Testing - does everyone do it?

    If your inspecting a new installation then you should be doing r1+r2 on every point (to prove earth cont and correct connection of accessories ) and then Zs the last point in the circuit to prove the Zs reading will give you 0.4 (0.2 on tt system) disconnection (unless an rcd is in circuit). On...