Recent content by rayelect

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.
  1. R

    Electrical Instalation condition report codes details

    Cicuit 1 is the garage cicuit 2  is a spare . not connected 
  2. R

    Electrical Instalation condition report codes details

    The light was IP44  when installed few years ago so presume good for zone 2. Although I did see what looks like dead flies in the bottom. I presume through the wiring gap form the loft above. Would this indicate the light is no longer IP44 rated as flies got in. I went round today and moved the...
  3. R

    Electrical Instalation condition report codes details

    What constitutes a zone 1 for a bathroom light .? The bathroom light is 221cm off floor but just outside the footprint of the bath (within the 600m of zone 2). But the bath has one of those spring shower curtain rails across the walls and curves out near the middle. At the curve it comes under...
  4. R

    Electrical Instalation condition report codes details

    Only one Schedule test result sheet. I know they tested the garage as I had to open it to let one of the guys in to test.. Scary thing is he was teaching an apprentice as well.  I think I need to pursue a refund and get it all done again by a local electrician. 
  5. R

    Electrical Instalation condition report codes details

    There is armoured cable to a small fuse box in the garage with 2 lights and socket. There is a garage consumer unit with RDC, 6mcb and 16mcb. Fuse Box is split with Lights downstairs has own RCBO and Garage MCB to garage consumer unit RCD. 
  6. R

    Electrical Instalation condition report codes details

    So I emailed again for more information and had a reply of  - 'Please see attached picture of light which need to be replaced, and the no continuity is on the ring main, sockets' Line and neutral.  so narrowed it down to the ring main. Would that be considered sufficient information to identify...
  7. R

    Electrical Instalation condition report codes details

    Yes there is a schedule of test results  -  all 6 circuits have R1+R2 circuit impedances ranging between 0.49 and 0.84ohms. Only Socket ring  has  - r1 0.23, rn 0.23, r2(cpc) 0.38. The electrician was appointed through a known (tv adds) nation wide online rental agent. 
  8. R

    Electrical Instalation condition report codes details

    I have asked for further information on the observations and got a quote.  Stating  -1. Investigate no continuity online and neutral. 2 Replace bathroom light. £190 I fear on them not giving out further information I am being forced into using them to do the works. If I got someone else do they...
  9. R

    Electrical Instalation condition report codes details

     Would this refer to a loose wiring. I did see them take off a socket in the kitchen . 
  10. R

    Electrical Instalation condition report codes details

    Thanks. 701.512.2 applies to electrical accessories in zone 0 or zone 1.. The bathroom light is probably just within the 600mm from the edge of the bath but definitely not over the bath. ceiling of about 2300mm. Even in zone 1 would  IP44 be be ok ?? Would lights come under accessories ?
  11. R

    Electrical Instalation condition report codes details

    I recently had a EIRC done for a rental. After the checks I asked the electrician if all was OK, and he refusing to say anything just referring me back to 'the office will send a report'?? Which I thought odd as I'm paying for the report. It came back  today as unsatisfactory (code C2) There...
Top