PVC conduit in escape routes

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Luckyboy

Well-known member
Joined
Sep 18, 2021
Messages
111
Reaction score
22
Location
London
Hello
I'm planning an emergency lighting circuit for a communal domestic setting.
Someone's already fitted PVC trunking for the fire alarm system, hopefully with steel clips within...

Is it bad practice if I were to fit PVC conduit, if fitted with steel saddles? for the purpose of emergency escape routes.
I don't want to fit steel conduit throughout as it won't look nice aesthetically.
 
Assuming you are installing to amendment 2 then the containment must not propagate when exposed to a flame. I would personally use FP200.
 
so is the way to go just clipped direct with FP200 with metal clips although the uPVC stuff doesn't actually contribute towards a fire?
 
You need to check your design with the responsible fire engineering team.
If the route is a formal protected escape route, then PVC conduit is unlikely to be acceptable surface run through the area.
 
You need to check your design with the responsible fire engineering team.
If the route is a formal protected escape route, then PVC conduit is unlikely to be acceptable surface run through the area.
Never heard of a formal protected escape route?
 
definition : protected escape route (page 40 in amd 2) - points you to Escape route

definition : Escape route (page 35 in amd 2) - points you to protected escape route)

Fabulous:)

I'm thinking that very few people need to get involved in this!
No they aren't defining them as such just bouncing you back and forth. Not all escape routes are 'protected' for example a circulation space may have routes to a stairwell escape and whilst the stairwell maybe 'protected' the route to it isn't.
 
A protected escape route is apparently a common term in fire engineering.
The definition of such locations is not the responsibility of the electrical designers or contractors.
It is down to the fire engineering/strategy for the building and is the responsibility of the fire design organisation and the building client/architect.
 
K
A protected escape route is apparently a common term in fire engineering.
The definition of such locations is not the responsibility of the electrical designers or contractors.
It is down to the fire engineering/strategy for the building and is the responsibility of the fire design organisation and the building client/architect.
I know about the types of escape route but where in BS7671 does it state formal protected route.
 
K

I know about the types of escape route but where in BS7671 does it state formal protected route.
I don't think you will find that in BS7671, it's a term from fire alarm standards. The NICEIC changed the AC status a few years ago not to include fire protection systems, in reflection of the fact few sparkies knew the appropriate standards well enough. I was rather annoyed by that at the time, but now think they may have had a point 😄
 