Search results

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.
  1. H

    Cant get Ra <200ohms

    Ring the local supply company , I've come across unrodded tranformers , or nicked rods and cables at the suppliers transformers . Especially on transformers mounted on poles . But sometimes it's just down to the location. As long as it complies with bs 7671 and the touch voltage rule then there...
  2. H

    fault finding

    AM2 , acheivement measurement 2. Under city and guilds , apprentices sit 2 AM tests . An AM1 and AM2 , an AM1 is usually sat after the first year and is used to check basic circuit knowledge and clipping t+e , bending radii etc . AM2 involves a complete installation within a set timeframe ...
  3. H

    Zs live Testing - does everyone do it?

    If your inspecting a new installation then you should be doing r1+r2 on every point (to prove earth cont and correct connection of accessories ) and then Zs the last point in the circuit to prove the Zs reading will give you 0.4 (0.2 on tt system) disconnection (unless an rcd is in circuit). On...
Top