  1. gc100

    Minimum Kva/Amps for a new build

    Thanks. I did call several but they was only interested in commercial. None of them wanted anything to do with domestic (I suppose its the same for Uk Power Networks!)
  2. gc100

    Minimum Kva/Amps for a new build

    Wow thats really interesting!! Just to clarify, I have several options. Both in terms of the total KVA needed and the setup with the DNO. They are happy to put a kiosk at the edge of the land , which would then mean a 600m odd run to the barn. They are also happy to do it all the way to the barn...
  3. gc100

    Minimum Kva/Amps for a new build

    Thanks. I have spoken to the DNO - they suggested this route. Their quote was £40K for a 40kVa which is too much both in power and cost!. The nearest transformer is 600 odd meters away, and its only a 16KvA transformer feeding an existing customer. They have told me they will need to upgrade...
  4. gc100

    Minimum Kva/Amps for a new build

    Hi, first post- I'm not an electrician and have spoken to my local one about this, but he didn't offer much opinion so I thought I would ask here. I'm converting a barn in open countryside and its about a 600meter run from the nearest transformer. If we go with a 100amp single phase (I'm told...