  1. K

    Is this a spur off of a spur?

    Cheers. The problem I have with extending the ring is that the 'parent' socket is only a 1G with a 25mm box, meaning that 3 cables will be tight, whereas 4 cables and joins would be nigh on impossible. I could always channel out a larger space but that is already a finished surface etc etc... I...
  2. K

    Is this a spur off of a spur?

    Thanks for the quick replies. I'll think about extended the ring, although this would require a cable join would it not? If so how would this best be done? So could I still wire in the new socket and the fire on the 'load' side of the FCU? This way the whole spur would be fused at 13amp.
  3. K

    Is this a spur off of a spur?

    Hi, Need some advice on the fitting of an FCU and a socket to en existing ring final. Basically I'm aiming to spur an FCU from an existing socket in my lounge. This FCU will be used for a wall mounted fire drawing no more than 6.5 amps. Whilst I'm at it I thought I may also add a double...