Sorry Iam yrying to work out K factor for a consumer mains & sub mains
CM 300mm
SM 50mm
K factor as per AS/NZ 3008 for 300mm V75 = 111
I have worked out ( with a little help )
S = Sqrt of Isq X T/Ksq
CM = 7143X7143X2/111X111 = 91mm
SM = 5523X5523X1/111X111 = 49.75 mm
Iam trying to...
Ok fellas thanks for the replys before, but can you check/help with this.
t = Ksq X Ssq/Isq ?????
t = 111 X 111 X 300 X 300/7143 X 7143 = 21.80 sec
S = 300mm consumer mains
t = 111 X 111 X 50 X 50/5523 X 5523 = 1.08 sec
Is this correct or near ???? t = the time it will take before the...
Morning all, ant one care to explain/help with this ????
S= current sq x t
K sq
Current is it fault/design ???
Fault current sq ( 7137 x 2) X 2 secs
( 111x2 )
= 14274/222 = 64.29 mm
Thanks Steptoe, Z at the submain/PA or both added toghether ??
If I have impedences of,
Z1 transformer imp 0.01591
Z2 Consumer mains 0.0037 3
Z3 submains to DB 0.026
I think AMP=Z1+Z2+Z3/ is it sph or 3ph after this I loose the will to live !!!!!.
Thanks Steptoe, but I was after the for formula !!! I just can`t seem to get it in my head for some reason !!!!!. :coat :coat:coat:coat:coat:coat:coat:coat:coat
Hi Iam a mature apprentice in Western Australia and Iam struggling with PFC & PSC can any one help me pls, I have been told by a guy from the UK this is the site to be on.
Regards Downundersparky.