  1. T

    3kW heater - 2.5mm T+E - 32A MCB?

    Good Morning Fleeting, I did think this, hence my original thought to isolate the circuit for now, but when doubting my Friday afternoon clarity of thought a discussion with some other wiser (?) colleagues lead to advice to treat the heater as a fixed resistive load....but as you say, if there...
  2. T

    3kW heater - 2.5mm T+E - 32A MCB?

    Thanks binky....the 13A fused switch had definite signs of overheating (running at close to 13A for close to 10 hours a day) but had not melted as I've often seen when an immersion heater has been wired through a FS, so I would definitely want to swap out for a 20A switch. If we are saying that...
  3. T

    3kW heater - 2.5mm T+E - 32A MCB?

    Good Morning All. Emergency call to local charity shop yesterday due to "no heating". 3 x 3kW "curtain heaters" on site, 4 of these on individual 16a MCB with 2.5mm T+E to 20A control switch...happy days, replace damaged control switch for 2 of these which had been damaged by being knocked...
  4. T

    Fault finding lights

    Thank you all for your swift replies....landing it is to start with then...I have the ferret cam on standby! I'll let you know how it goes!
  5. T

    Fault finding lights

    Good morning all. Would appreciate your thoughts on the following. Call out yesterday to 1970's domestic property with 50% of ground floor lights not working, no MCB trip (lights not RCD protected). I was hoping for a relatively straightforward binary search, checking at ceiling roses for a...
  6. T

    EICR - Structural Steel Main Protective Bonding

    Thanks Fleeting.....and that's why I come on the site....sometimes the answer is staring you right in the face but you're so close you can't see it without someone else pointing it out!
  7. T

    EICR - Structural Steel Main Protective Bonding

    I believe the 0.05Ω figure comes from GN8. I take your point regarding the isolation / parallel paths. Question remains whether my continuity measurement of 0.22Ω is sufficiently low to consider it "evidence" of a hidden MPB to the structural steel, or whether I should indeed be recommending...
  8. T

    EICR - Structural Steel Main Protective Bonding

    EICR on commercial premises approx 8 yrs old. Structural steel is confirmed by test as extraneous conductive part. No EIC / paperwork available. MPB to gas / water services confirmed visually and by measurement - 1 continuous conductor serves both. Unable to visually locate MPB to structural...