  1. G

    Distribution Circuit on DNO fuses.

    Thanks Sidewinder, just trying to find confirmation 'online' to show the owner but cant seem to locate .....  any ideas where I might find confirmation? FI - The meter tails are less than 3m in length, its just the issue of protecting the 16mm 4c cable.
  2. G

    Distribution Circuit on DNO fuses.

    That would do it but is there anything against using the DNO fuses to provide OC protection?
  3. G

    Distribution Circuit on DNO fuses.

    I looked at a job recently where a distribution circuit was feeding a 3ph dist board some 10m away. My concern is that the only protection for the cable is by the DNO fuses (Labelled at 1361 100A - sealed so unable to confirm) Cable is 16sq 4c clipped direct and rated at 94A (Table 4E4A - BS...
  4. G

    Outdoor Lighting

    Thanks for that Lurch, shall save me going out and buying a copy.
  5. G

    Outdoor Lighting

    I'm currently looking at a project where 'ground recessed lights' are being specified and on checking the Regs. section 714.512.3 "Ground-recessed luminaires" recommends taking account of guidance provided in Table A.1 of BS EN 60598-2-13. Without blowing nearly a ton on a standard I may never...