Search results

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.
  1. K

    Switching / wiring advice for Megaflow with 4x 3kw immersions?

    Regulations are a guidance not laws, in the Regs themselves it's stated use common sense. Like I said above which I hope you read and if you have done any testing and inspection one of the things to note on your certificate if there's a dual supply you need to have to put a yellow sticker of...
  2. K

    Boiler Thermostat

    Thank you for the reply. I have already taken care of the technical side which your questions are pointing to. Both conditions above are satisfied. Both cables are can run alongside each other. The thermostat cable is shielded so no interference and it is designed fort he job. My question is can...
  3. K

    Switching / wiring advice for Megaflow with 4x 3kw immersions?

    Hi 64sp, I am sure this forum is leaving you more confused than when you started. The illustrious members of this forum with to many answers have a strong Domestic installations bias. You will need a Commercial electrician to do your job not a Domestic one or one who is experienced in both...
  4. K

    Switching / wiring advice for Megaflow with 4x 3kw immersions?

    4 separate immersion heaters on one unit. When you hit the isolator you expect that unit to be off not is there anything else I have to switch off? It is just bad practice to do that. Have you ever come accross the yellow label "Caution fed from elsewhere, dual supply" ?
  5. K

    Switching / wiring advice for Megaflow with 4x 3kw immersions?

    4 separate supplies to one unit. Although it has 4 different load intakes, it is still one unit.
  6. K

    Socket within 300mm of gas cooker

    From memory an electrical point should be at least 150mm away from services of any type. 300mm is above the counter as mentioned above. Blanking is usually enough. Out of curiosity are you replacing oven and hob from electric to gas, is it two separate units hob and oven or one unit made of oven...
  7. K

    Switching / wiring advice for Megaflow with 4x 3kw immersions?

    You don't need four radials. One is needed as long as it's able to carry the load of all 4 and that will supply 4 contactors, then each contactor will supply each element. 4 radials would make it dangerous.
  8. K

    Boiler Thermostat

    From a Regs point of view, is it allowed to run a thermostat cable(bell cable) inside the same outlet as the boiler flex outlet? In the picture attached the twin and earth does the flex outlet point for the boiler and on the right there's the bell cable doing the thermostat. My question is...
  9. K

    Switching / wiring advice for Megaflow with 4x 3kw immersions?

    From your description you have a single phase water heater with 4 individual elements. This should have been more suitable on a three phase supply type of water heater. But three phase supply is not so common on domestic installations. The nature of your power supply should have determined what...
  10. K

    Domestic fire alarm with fault outputs

    Ok, lol. The long answer would be 24V is low voltage no need to run twin and earth or power cable fit to carry up to 600V. Low voltage cable would be enough.
  11. K

    Domestic fire alarm with fault outputs

    Thank you. Hush-active looks very promising. It's also 24V so no need to run twin and earth or power cables. Aico will check as well.
  12. K

    Domestic fire alarm with fault outputs

    I'm looking for a BS5839:6 Grade A or C basically a domestic fire alarm system. Am looking for a complete kit. There is no panel, that's what I'm looking for. Apologies for the confusion the "Fault" word as Kerching says above is wide reaching. So it's about terminology, by fault I was meaning...
  13. K

    Domestic fire alarm with fault outputs

    I will give this a try. Looks like best solution so far, Maybe use a spare interconnected sounder to engage a relay for the output. Resetting it, through an input still a question unless provided by panel itself. To my knowledge domestic fire alarms are self-ressetting usually.
  14. K

    Domestic fire alarm with fault outputs

    Fault = Panel goes to fault- Sounders triggered - alarm goes off
  15. K

    Ring main return cable route

    Thank you to all who provided constructive feedback. And to the cynics in this forum for making the thread amusing.
  16. K

    Ring main return cable route

    You make me laugh with your assumptions. Wrong: Not knowing how to run a ring main Are you saying Mike.J is wrong? Not knowing how to "get around" the issue of a cable in a wall where it would not be expected by sticking another socket Not an issue: Running cables through a 25mm box and reducing...
Top