  1. J

    No Earth

    DNO tested there end and said its fine...all sorted now...if it comes disconnected in the future it is what it is...they can sort that if and when it happens
  2. J

    No Earth

    The electrician who rewired the property said he new someone from manweb who will sort it as a foreigner....go figure
  3. J

    No Earth

    We were only there to check a possible dodgy socket which then led from one thing to another...why would you leave a job that is potentially dangerous just because you think you will get implicated in someway...calls were made everyone on site at the same time...issues rectified installation now...
  4. J

    No Earth

    Will get client to send some over and post 😊
  5. J

    No Earth

    I don't think there is any cover up..the lady was showing payment details to the lads from the DNO...she said they had used him multiple times
  6. J

    No Earth

    Yes..put board on wall also....B Gas put new meter on...isolator in place also
  7. J

    No Earth

    Well that's what he said...didn't think there would have been 3 meters of slack from outside..inside was concrete floors
  8. J

    No Earth

    Apparently so...they have used him before..said they picked up a flyer @ Taskers for his company
  9. J

    No Earth

    Yes....apparently its bee like that since June 22....client said they are going to send a bill back to him...apparently he's living in a B&B in Wales..😵‍💫
  10. J

    No Earth

    Not sure apparently he suffered a break down client produced paper work to confirm payment of £700 to move incoming....DNO said it must have been jointed and screened over when underfloor heating (water) was installed as there would not of been 3 metres of slack to pull through...british gas...
  11. J

    No Earth

    It's done..DNO came...plate connecting earth to neutral was missing in the incoming head
  12. J

    No Earth

    I'm going to put a temporary TT in and call DNO & meter company see what happens..I'm thinking cable damage..Ze is coming back 550...managed to get 0.16 Zs when piggy back neutral & earth but that's with just the gas connection to earth once I put main earth in from incoming head it reads...
  13. J

    No Earth

    I'm going back tomorrow to investigate further before I make a decision on what to do..will take more pictures
  14. J

    No Earth

    Sure can 😅
  15. J

    No Earth

    Yes earth to gas
  16. J

    No Earth

    Yes to gas ...no to water 👍🏻
  17. J

    No Earth

    Probably TNS...although TNCS are in Properties in the area also
  18. J

    No Earth

    TT so at least they have something & and call DNO to sort the head & meter out
  19. J

    No Earth

    To gas not water..water is plastic incoming
  20. J

    No Earth

    So if it was you would you convert to TT or call DNO & meter company