    R1 R2 values fluctuate over time

    Bare with me people as I try to explain this. Currently working on a site, been responsible for testing under floor power tracks that are fed in 3 core 10mm swa on 32a mcb. Tested a bunch of them maybe 4-5 weeks ago. Got the results all happy days. In work this week I was informed a separate...
  2. G

    Phantom voltage?

    Yeah I’ll give it another look Monday. Connect the fittings in see what happens
  3. G

    Phantom voltage?

    I’ll give it a try Monday mate, just didn’t want to finish the job without an other opinion and making sure. Nice one 👍
  4. G

    Phantom voltage?

    I have, reading was 2.10 brown-earth 2.11 black-earth, would a cpc not connected send voltage down the SL? Because nothings plugged into the kliks they’re essentially just connector blocks at the moment so no way of voltage back feeding down the SL from the PL? I thought maybe a loose neutral...
  5. G

    Phantom voltage?

    I did type this out and send it about 2hrs ago but I can’t see it on the forum so I’ll post again. Came across a weird *fault* if you’d call it that, basically stripped out old lights in a warehouse, switch fed so perm live and neutral at the switch. Wired a 3core and earth to 18 4pin klik...