Please use this thread for discussion on the changes in the 18th Edition.
So excluding all the pre-amble up to part 1.
Part 1.
110.1, xxvii has been added, "onshore units of electrical shore connections for inland navigation vessels"
This covers the connection points for things like river cruise ships, canal boats, or river taxis, marinas are already covered in a section.
Right through the document a.c. & d.c. have been changed to AC & DC for harmonisation with the IEC documents. I am not going to include any changes related to this.
I'm either going to colour the new bits blue, or explain them, depending on which is the easiest.
So if it's blue it's added, if it's red it's deleted, else it will be explained.
110.1.3, iv has had a standard changed BS EN 61241 has been replaced by BS EN IEC 60079 series, as the 61241 series has been replaced by the 60079 series for equipment in the presence of combustible dust, so we have moved away from EU harmonisation to harmonising with the IEC requirements.
110.2 "Exclusions from scope", has a few changes.
(iv) Equipment on board ships covered by BS 8450, BS EN 60092-507, BS EN ISO 13297 or BS EN ISO 10133
(x) Those aspects of lift installations covered by relevant parts of BS 5655 and BS EN 81 and those aspects of escalator or moving walk installations covered by relevant parts of BS 5656 and BS EN 115
113 no changes
114, relationship with statutory regulations, has had the dated reference to ESQCR removed, and changes relating to the re-structuring of the layout.
115 no changes
Ch 12.
120.1 This Standard contains the rules for the design,and erection and verification of electrical installations so as to provide for safety and proper functioning for the intended use.
120.3 This Standard sets out technical requirements to enableintended to ensure that electrical installations to conform to with the fundamental principles of Chapter 13, as follows:
The comment at the end of 120.3 has the wording changed such that it is now required to record any deviations on an EIC, but the requirement is still that deviations shall provide the same level of safety as compliance.
131.2.1 & 131.2.1 have had "(protection against direct contact)" deleted from the end of the line.
Throughout changes noted that occurred in 17th Amd3 have been removed.
132.2, (iii), 4th indent, — prospectiveshort-circuit fault current
132.8 Protective equipment
The characteristics of protective equipment shall be determined with respect to their function, including protection against the effects of:
(i)overcurrent (overload and/or short-circuit)
(ii)earth fault current
132.12 Accessibility of electrical equipment
Electrical equipment shall be arrangedso as to afford as may be necessary to provide:
133.1.3 Where equipment to be used is not in accordance with Regulation 133.1.1 or is used outside the scope of its standard, the designer or other person responsible for specifying the installation shall confirm that the equipment provides at least the same degree of safety as that afforded by compliance with the Regulations. Such useis to be noted on the Electrical Installation Certificate shall be recorded on the appropriate electrical certification specified in Part 6.
Note the change in wording in 133.1.3, this is strengthened, it is "shall", which in legal and standards parlance is you must do, I realise that 7671 is not law, but if you are going to claim compliance with HASAWA & EAWR by following BS 7671, then, you must, do the shall clauses.
134.1.1 Good workmanship by one or more skilled or instructed persons and proper materials shall be used in the erection of the electrical installation. The installation of electrical equipment shall take account of manufacturers' instructions.
134.2 has been changed to reflect I&T being moved to Ch 64 & 65.
That's part 1 finished.
Part 2, definitions
Any definitions that were removed by previous versions have been removed.
Also the following changes:
Back-up protection.
Protection which is intended to operate when a system fault is not cleared, or abnormal condition not detected, in the required time because of failure or inability of other protection to operate or failure of the appropriate circuit-breaker(s) to trip.Protection of a device by overcurrent co-ordination between that device and an overcurrent protective device (OCPD) in series with it, generally but not necessarily on the supply side. This prevents any excessive stress on the electrical device.
Discrimination.
Ability of a protective device to operate in preference to another protective device in series.(see Selectivity)
Follow-current interrupting rating, {534}Ifi.
The level of pProspective short-circuit current that an SPD is able to interrupt without back-up protectionoperation of the OCPD
Isolation.
A functionFunction intended to cut offmake dead for reasons of safety the supply from all, or a discrete section, of the electrical installation by separating the electrical installation, or section thereof, from every source of electrical energy.
Monitoring.
Observation of the operation of a system or part of a system to verify correct functioning or detect incorrect functioning by measuring system variables and comparing the measured values with specified values.
Protective multiple earthing (PME).
An earthing arrangement, found in TN-C-S systems, in which the supply neutral conductor is used to connect the earthing conductor of an installation with Earth, in accordance with the Electricity Safety, Quality and Continuity Regulations (ESQCR)2002 (see also Figure 3.9).
Residual current device (RCD).
A mMechanical switching device designed to make, carry and break currents under normal service conditions andor association of devices intended to cause the opening of the contacts when the residual current attains a given value under specified conditions.
Selectivity.
(see Discrimination).Co-ordination of the operating characteristics of two or more protective devices such that, on the incidence of an overcurrent or residual current within stated limits, the device intended to operate within these limits does so, while the other(s) does (do) not.
Switch.
A mechanical device capable of making, carrying and breaking current under normal circuit conditions, which may include specified operating overload conditions, and also of carrying for a specified time currents under specified abnormal circuit conditions such as those of short-circuit. It may also be capable of making, but not breaking, short-circuit currents.
Part 1.
113 no changes
115 no changes
Ch 12.
(i)
(ii)
Part 2, definitions
Back-up protection.
Discrimination.
Isolation.
Selectivity.