Timotei
Member
Good Morning All.
Emergency call to local charity shop yesterday due to "no heating".
3 x 3kW "curtain heaters" on site, 4 of these on individual 16a MCB with 2.5mm T+E to 20A control switch...happy days, replace damaged control switch for 2 of these which had been damaged by being knocked (plastic replaced with metal clad).
The remaining 2 heaters are on 1 circuit, each run in 2.5mm T+E from a 32A MCB. The first (operating normally) runs to a 20A control switch, the second (not working) runs to a 13A fused switch. I was going to change the FS for a 20A control switch as overheating of the fuse has caused minor damage to the switch mechanism.....but then found that both are on the 32A MCB....at this point Friday Afternoon Fever kicked in.....so, is this all good because the heaters are a fixed resistive load and Reg 433.3.1(ii) applies.....or does basic circuit design require that the MCB provides both overload and short circuit protection to the 2 x 2.5mm cables, so 20A or 16A MCB?
At the time my instinct was that the heaters should be split to individual circuits with 16A MCBs (there are no spare ways in the DB), and as all 4 other heaters are now working I recommended that this circuit be left isolated and the heaters not used....however, after looking at the quoted reg last night, I now think I may have over-reacted, and that as the conductor "is not likely to carry overload current", the existing setup (minus the FS) is good to continue......although i would want to verify that there are no spurs from the circuit between DB and heaters (shop open while I was there and not possible to access all sockets...the shop manager did say that the sockets seem to have no logical pattern of which circuit they are on).
EICR due in April, and I have said that as well as carrying out the EICR I will take time to fully label each socket outlet / switch etc with DB and circuit numbers.
I would appreciate your thoughts.
Timotei
Emergency call to local charity shop yesterday due to "no heating".
3 x 3kW "curtain heaters" on site, 4 of these on individual 16a MCB with 2.5mm T+E to 20A control switch...happy days, replace damaged control switch for 2 of these which had been damaged by being knocked (plastic replaced with metal clad).
The remaining 2 heaters are on 1 circuit, each run in 2.5mm T+E from a 32A MCB. The first (operating normally) runs to a 20A control switch, the second (not working) runs to a 13A fused switch. I was going to change the FS for a 20A control switch as overheating of the fuse has caused minor damage to the switch mechanism.....but then found that both are on the 32A MCB....at this point Friday Afternoon Fever kicked in.....so, is this all good because the heaters are a fixed resistive load and Reg 433.3.1(ii) applies.....or does basic circuit design require that the MCB provides both overload and short circuit protection to the 2 x 2.5mm cables, so 20A or 16A MCB?
At the time my instinct was that the heaters should be split to individual circuits with 16A MCBs (there are no spare ways in the DB), and as all 4 other heaters are now working I recommended that this circuit be left isolated and the heaters not used....however, after looking at the quoted reg last night, I now think I may have over-reacted, and that as the conductor "is not likely to carry overload current", the existing setup (minus the FS) is good to continue......although i would want to verify that there are no spurs from the circuit between DB and heaters (shop open while I was there and not possible to access all sockets...the shop manager did say that the sockets seem to have no logical pattern of which circuit they are on).
EICR due in April, and I have said that as well as carrying out the EICR I will take time to fully label each socket outlet / switch etc with DB and circuit numbers.
I would appreciate your thoughts.
Timotei