2 single core cables having a resistance of 1.2 ohms and 0.16, are connected in parrallel and are used to carry atotal current of 30A. Calculate (A) volt drop on the cables, (B) the actual current carried by each cable.
the usuall terms of payment for this one fellas !!!!!!!!!!!!
regards Iain
The Godfather
Retired
Joined
Mar 24, 2008
Messages
1,302
Reaction score
0
2 single core cables having a resistance of 1.2 ohms and 0.16, are connected in parrallel and are used to carry atotal current of 30A. Calculate (A) volt drop on the cables, (B) the actual current carried by each cable.the usuall terms of payment for this one fellas !!!!!!!!!!!!
regards Iain
Firstly the actual resistance is:
1.2 x 0.16 / 1.2 + 0.16 = 0.1411764 ohms
So @ 30A Vdrop is 30 x 0.1411764 = 4.235292V (use this voltage divided by each of the resistors to find the current flowing through each one)
First cable 1.2 ohms carries 3.52941A, the second cable carries 26.470575A approx
Which when added together give 29.999985A