Got a cu to change so dropped in to customers, to do a quick test prior to swap next week.

Cover off...Hmm harmonised colours on ring but only a 20amp mcb (oh what problems will I find)?

customer pipes up " oh the last electrican put those cables in when they fitted the kitchen, that fuse always trips when I have the kettle on at the same time as the washing machine & dryer"

r2 = 0.92

rn = 0.51

r1 = 42

Thats the largest r1 I've seen for a while.

looked at the kitchen all integrated appliances no isolation above worktops :_|

No ccu for oven/hob again all integrated units, so gotta dismantle kitchen to test circuit :_|

Service head & meter hanging off the wall & fuse carrier + neutral link casing cracked, uninsulated live components on show, all this is at floor level in the lounge not boxed & the couple living here have a 2 yearold wandering about :eek:

They just couldnt grasp how dangerous it is.

Oh deep joy...told em they gotta get the service head sorted before I'll do anything on the cu.

Time for another beer!!!!! :D

 

seajayess

Senior Member
Joined
May 28, 2008
Messages
272
Reaction score
0
The r1 reading must be bad connection somewhere as that reading would equate to around 5668 meters in lenth CJS :)

 

M107

Billy-the-Kid
Joined
Feb 18, 2008
Messages
5,562
Reaction score
28
Location
Berkshire
The r1 reading must be bad connection somewhere as that reading would equate to around 5668 meters in lenth CJS :)
Yes I know & you can just bet a months money it's behind the integrated kitchen kit. :(

 

The Godfather

Retired
Joined
Mar 24, 2008
Messages
1,302
Reaction score
0
Once you know there is a problem with the service HED, then any other work is academic.

(Until resolved)

The Boys

(Don's back soon)

 

M107

Billy-the-Kid
Joined
Feb 18, 2008
Messages
5,562
Reaction score
28
Location
Berkshire
Once you know there is a problem with the service HED, then any other work is academic.(Until resolved)

The Boys

(Don's back soon)
Thats what I told the customer. SSE are attending Wednesday to change the hed/meter & fit an isolator.

 