are rcds supplementary protection

Help Support Talk Electrician Forum:

chrisgjudd

Junior Member
Joined
Apr 18, 2008
Messages
15
Reaction score
0
newbie needs to clarify if you have a 17th edition split load rcd consumer unit on a tt system which circuits should be rcd checked at 5 times trip current, and now that we have to rcd protect cables less than 50mm in walls does this mean the rcds used are supplementary protection.Or is it just were disconnection times cannot be met....?? ]:)

chrisgjudd

 
Joined
Mar 7, 2008
Messages
9,994
Reaction score
0
Location
In the office again.
newbie needs to clarify if you have a 17th edition split load rcd consumer unit on a tt system which circuits should be rcd checked at 5 times trip current, and now that we have to rcd protect cables less than 50mm in walls does this mean the rcds used are supplementary protection.Or is it just were disconnection times cannot be met....?? ]:) chrisgjudd
All the RCD`s / RCBO`s need to be checked at 5x, as long as they`re 30mA or less.

Yes, the RCD is supplemental anyway; but can be basic protection too; esp. on a TT.

HTH

KME

 
Joined
Mar 28, 2008
Messages
13,621
Reaction score
297
newbie needs to clarify if you have a 17th edition split load rcd consumer unit on a tt system which circuits should be rcd checked at 5 times trip current, and now that we have to rcd protect cables less than 50mm in walls does this mean the rcds used are supplementary protection.Or is it just were disconnection times cannot be met....?? ]:) chrisgjudd
Deja Vue?? ; \ ]:)

 
Joined
Apr 13, 2008
Messages
70
Reaction score
0
Ha ha I am now here!

Fancy that posting the same question twice.

I think KME has anwered your question clearly. :)

Better go now its getting late.

 