Hi all, really hope someone can help me as I am doing something wrong when it comes to cable calcs, I am currently working my way through my lvl 3 EAL. Would someone be able to work through this question so i can see where i am potentially going wrong. Thanks in advance.
TN C S = 0.35
Ambient temp = 20
3ph DB (BS EN 60898)
3ph circuit for car lift, wired in pvc singles in trunking with 3 other circuits, circuit length 8M.
3 ph supply to a two post vehicle lift: 400 V 3 kW with a p.f of 0.85,
My calcs so far:
3000/ 1.732x4000.85 =
Ib = 5.094A
In = 6A (type C) (6A ≥5.094A)
6A/0.65(cg)
Iz = 9.23A
It = Cable Size = 1mm2
38x5.094x8/1000 =
Voltage drop = 1.54V
36.20(R1+R2) x 1.20(multiplier table I3 OSG) x 8 / 1000 = 0.34
0.34+0.35(Ze) =
Zs = 0.69
230/0.69 =
Isc = 333A
Adiabatic (0.2s as 3ph?) = 1.29mm (needs to be same or smaller than line?)
I must be doing something wrong, please help.
TN C S = 0.35
Ambient temp = 20
3ph DB (BS EN 60898)
3ph circuit for car lift, wired in pvc singles in trunking with 3 other circuits, circuit length 8M.
3 ph supply to a two post vehicle lift: 400 V 3 kW with a p.f of 0.85,
My calcs so far:
3000/ 1.732x4000.85 =
Ib = 5.094A
In = 6A (type C) (6A ≥5.094A)
6A/0.65(cg)
Iz = 9.23A
It = Cable Size = 1mm2
38x5.094x8/1000 =
Voltage drop = 1.54V
36.20(R1+R2) x 1.20(multiplier table I3 OSG) x 8 / 1000 = 0.34
0.34+0.35(Ze) =
Zs = 0.69
230/0.69 =
Isc = 333A
Adiabatic (0.2s as 3ph?) = 1.29mm (needs to be same or smaller than line?)
I must be doing something wrong, please help.