Cable Calculations
Puthor
Oct 19, 2011
9
Hello i need some help with the cable calcuations.
The question is as followd
Lighting Circuit (12 lamps)
Domestic House
Type B Circuit Breaker
Clipped Directly to wooden joist
-(above plasterboard ceiling coverd by thermal insulation exceding 100mm thikness)
Flat twin & earth cable
30 meters lenght of circuit
TNC supply
Ib=
In=
It=
Iz=
Vd=
R1&R2=
Zs=
If=
s=
When i try to solve it i get.
Lighting Circuit (12 lamps) = 1200
Domestic House = 230v
Ib=5.2
In=6a (But i dont know witch one. Closest is 6a but in BS7671 there is 4 diferent circit brakers. It cant be the C and D so is it the "Type B Circuit-Braker to BS EN 60898" or is it "Fuses to BS 88-2.2 and BS 88-6"
It= In/Cc*Ci*Cg*Ca*Cr (But i dont need to use the Cc or Cr right?) It say nothing about the "Ambient Temperature" do that mean is 1? and same with "Grouping" 1? The "Thermal Insulation" is that 10.5a 1mm cable?(page 282 BS7671)
In/Ci*Cg*Ca
6/1*1*?(10.5? or 1mm) I think its 10.5 but that be to high so 1?
=6?
(im prity sure somthing is wrong here)
Iz=1mm
44*5.2*30/1000
Vd=6.864
TNCS supply
R1&R2= 1.129
36.20*1.04*30/1000
Zs=7.67
If=29.98
(v(if^2*t))/k=s
(v(29.98^2*0.1))/115=0.082
s=0.082
It would help me very much if somone could tell me what im doing wrong. And how i can correct it. Thanks allot in advance.
Welcome to the forum Puthor, it is good to see you have had a go at answering some parts of your question yourself. Keep checking back here during the course of the day and I am sure someone will offer some help. Some of our members are out at work and may not get back till later so make sure you check back later in the evening or tomorrow morning for more answers. Why not go to our introduce yourself section and tell us a bit about who you are while you are waiting.
Aha. so "Ci" is 0.78
so it should be 6.6?
1. Ib 5.2
2. In 6
3. It 6.6
4. Iz 10.5 (Not sure im right here?)
5. Vd 6.864
6. R1&R2 1.129
7. Zs 7.67
8. If 29.98
9. s 0.082
Hi Phutor,
It is difficult to calculate without full details required, is this a :-
TN-C-S Max Zs = 0.35Ω
or a TN-S Max Zs = 0.8Ω?
Ib = P/V = 1200 (12 x 100w) / 230 = 5.2Amps
In = MCB type B = 6Amps
It = In/ Correction factors, see page 255 (brb) section 3 no correction factors reqd, so It = 6Amps
Iz = a Flat cable with CPC 70˚C with a CCC > 6 Amps, use table 4D5, Ref method is 101 above plasterboard with insulation exceeding 100mm, column 2, a 1mm cable CCC = 10.5Amps, look at voltage drop from same table column 7 = 44 Mv/A/M
Fault protection formula = Ib ≤ In ≤ Iz = 5.2A
I don't disagree with you Canoeboy, but could that rule of thumb be getting the boot with all of the different varieties of lamp that can now be gotten a hold of?AndyGuinness
I guess they are still using the 'allow 100watts per point rule', but as you say Zeespark, with retail outlets not selling 100watt lamps anymore it does seam a bit silly to say the least. Are 60watts also obsolete yet?
Thanks a lot!
That help a ton.
Yes sorry i ment a TNCS system
I tried another question after that but got stuck again.
But this one is to do with Iz (cable size)
12kW cooker with socket-outlet
Domestic House
Bs 3036 fuse
Enclosed in cnduit in an insulated wall
18 meters length of circuit
TNCS supply
The cable for "Enclosed in conduit in an insulated wall"( Method A ) for flat twin & earth is 57 at max but it needs to be 60 amps at least?
Am i not looking for the right cable?
1. Ib 52.17
2. In 60
3. It 60
4. Iz ?
Thanks a lot!That help a ton.
Domestic House
Bs 3036 fuse
TNCS supply
1. Ib 52.17
2. In 60
3. It 60
4. Iz ?
You will need to take Diversity into account with a cooker. The appliance rating is the value of all hob rings, grills, oven elements etc, but in the real world nobody has everything on at the same time. The On-site-guide has the recommended diversity values for cooking appliances. If you cant find it someone will probably add a table or page number later. Remember most domestic cookers work fine on a 30amp or 32amp fuse.
Thanks again that helped me alot. I hope i'm right now
So these 2 are correct?
Domestic House
Bs 3036 fuse
TNCS supply
1. Ib 27.65
2. In 30
3. It 30
4. Iz 6mm
5. Vd 3.63
6. R1&R2 0.22
7. Zs 0.57
8. If 403.5
9. s 1.569
Lighting circuit (12 lamps)
Domestic house
Type B circuit breaker
Clipped direct
Run through loft (45
Hi Puthor,
I am not sure about your adiabatic equation answer for scenario one,
show your calculation, so we can see how you get 1.569mm
everything else checks out fine,
(MEERKAT)
BRB page 245?
The fault current for this instalation is ony 403.5 and to trip a 30a in 0.1 sec it needs 450?
or am i doing somthing wrong?
diversity ?
its a good idea, but in the real REAL world, i know there ARE people out there that in the middle of winter, when the gas has run out, will put on just about every
electrical socket outlet and circuit that will generate heat, so thats diversity out of the window.
i'm taliking about nans and students lol.
then, and only then can they benefit from the underfloor heating i.e. the conducting twin and earth :p
Hi Puthor
BRB page 245?The fault current for this instalation is ony 403.5 and to trip a 30a in 0.1 sec it needs 450?
the scenario fault current is 403.5 Amps
450 Amps will trip fuse in 0.1 Sec's
300 Amps will trip fuse in 0.2 Sec's
therefore 403 Amps falls somewhere in between, ie 0.15 Sec's
I hope this helps,
(MEERKAT)