Off work with a bad case of leprosy and found this "circuit breaker " on a car forum.
I wonder...
I wonder...
But isn't that AC rated,?
and not DC,,,,,
It's the amps I'd be concerned about, not the voltage,Wouldn't matter at that low a voltage.
It's the amps I'd be concerned about, not the voltage,
Volts jolt
Current kills
But, i don't know tbh, I've always used DC switches on DC
In what sense?
he's probably using it as an MCB. well it does say 100A on it, in the same was some people think a 40a 30mA RCD will trip at 40a...
Rob, I'm sure you're a very intelligent bloke,The current carrying capacity is exactly the same AC or DC.
The reason items of equipment come with a DC rating is due to the nature of DC. It likes to produce an arc when broken under load. So DC rated equipment usually has larger contact separation or forms of arc quenching. From those batteries at 12V possibly 24V DC the seperation in the contacts will be more than good enough to extinguish the arc.
Rob, I'm sure you're a very intelligent bloke,
But, have you seen the size of an arc an even small DC welder can hold at <48v (that's what mine puts out), it's certainly iro 4or5mm , if not more.
As it was a factory fitted item to a fixed appliance, we were never quite sure how to document them on an inspection.
if its part of the appliance then its not covered by 7671 so your I&T ends at its supply