I have a EICR to do soon on a local community hall which i do small jobs for free as my family have been involved for years, but i want things to be correct (this report is being charged for) so would like to mention everything as they were shafted by a committee member over fairly recent electrical work carried out. Like a lot of recent threads on here, i cant be bothered to look anything up or rely on experience because its easier to ask you lot I mean i wondered what your views are on some items i know are existing.
A lot of the rooms have demountable ceilings with various light fittings that are all flexed to old 2 Amp plugs which do not have sleeved pins. Also the sockets (mainly the old round style fitted to conduit boxes & fed via MICC) do not have shutters on the holes ?
A fairly new fire alarm system was fitted mainly in self adhesive trunking that is falling off the walls. I know this does not meet BS5839 but can i mention it here ?
New emg ltg scheme, No external emergency lights on very dark rear fire escapes, once again is that something that should be mentioned here. ?
Also whole building wired to one new circuit for all emg ltg (that one i know, just mentioning it)
Now, how long till someone says 'the regs are not retrospective', so i can reply 'why is it we seem to pick and choose what we want to report'. You are inspecting to the current regulations.
There are some more when i remember them.
A lot of the rooms have demountable ceilings with various light fittings that are all flexed to old 2 Amp plugs which do not have sleeved pins. Also the sockets (mainly the old round style fitted to conduit boxes & fed via MICC) do not have shutters on the holes ?
A fairly new fire alarm system was fitted mainly in self adhesive trunking that is falling off the walls. I know this does not meet BS5839 but can i mention it here ?
New emg ltg scheme, No external emergency lights on very dark rear fire escapes, once again is that something that should be mentioned here. ?
Also whole building wired to one new circuit for all emg ltg (that one i know, just mentioning it)
Now, how long till someone says 'the regs are not retrospective', so i can reply 'why is it we seem to pick and choose what we want to report'. You are inspecting to the current regulations.
There are some more when i remember them.