Have any Electricians encountered problems converting a Crabtree Consumer unit to meet the 17th Edition.

seems that all their rcbo's are type C and their split boards only take 1 RCD on the split Bus bar.

 

kme

Fridge Keyholder™
Joined
Mar 7, 2008
Messages
9,987
Reaction score
0
Location
In the office again.
Have any Electricians encountered problems converting a Crabtree Consumer unit to meet the 17th Edition.seems that all their rcbo's are type C and their split boards only take 1 RCD on the split Bus bar.
So are wylex rcbos mate. C curve, that is.

 

wally

Gold Member
Joined
Mar 9, 2008
Messages
30
Reaction score
0
I have been told by Crabtree that type B will be some time yet, think there having problems, I agree, bit of a pain. Why not use the high integrity crabtree c/u with 2 rcds, problem if you need them for the non protected ways, will mean going back on job when they are available.

 

Krises

Junior Member
Joined
Jun 4, 2008
Messages
2
Reaction score
0
Thanks Wally,

First time I have encountered a Crabtree unit for certification to meet 17th Edition, you would think that they would supply a conversion kit for their existing units. WYLEX are much easier to convert.

 
Joined
Feb 27, 2008
Messages
11,030
Reaction score
0
Have any Electricians encountered problems converting a Crabtree Consumer unit to meet the 17th Edition.seems that all their rcbo's are type C and their split boards only take 1 RCD on the split Bus bar.
Hello krises

why not use mk there rcbos are b type they do two 17th edition consumer units and wf where doing there rcbos for

 

SPECIAL LOCATION

Trailer Boy - Electrician.
Joined
Mar 28, 2008
Messages
13,633
Reaction score
317
Have any Electricians encountered problems converting a Crabtree Consumer unit to meet the 17th Edition.seems that all their rcbo's are type C and their split boards only take 1 RCD on the split Bus bar.
Crabtree do a whole range of multi RCB boards and bus bar configurations..

many of them you have to order up special from your wholesaler.

Its more what the wholesaler stocks that what Crabtree make..

http://www.electrium.co.uk/Crabtree17thEdition(1).pdf

have a look at the above PDF around page 4ish?

Other PDFs you may want to look at..

http://www.electrium.co.uk/downloads.php

Or just go and check the product lists in the on-line-catalogue to see whats available..

http://www.electrium.co.uk/crabtree.htm

Oh by the way....

welcome ;)

 

steptoe

of course Im wrong, ask my wife™
Joined
Feb 13, 2008
Messages
24,422
Reaction score
162
Location
Gtr Manchester
stupid question time.

WTF is the difference?

in a normal domestic does a C and a B really make that much difference?

are you pushing the Zs that close?

I know the characteristics are different, but for a normal joe it should be fine, should it not.?

 

SPECIAL LOCATION

Trailer Boy - Electrician.
Joined
Mar 28, 2008
Messages
13,633
Reaction score
317
stupid question time.WTF is the difference?

in a normal domestic does a C and a B really make that much difference?

are you pushing the Zs that close?

I know the characteristics are different, but for a normal joe it should be fine, should it not.?
I would tend to agree with you there Steptoe.

P.S. can we borrow the horse for Saturdays water fight?

we want to do a sort of cavalry charge...

cum Roman gladiator chariot attack. ]:)

With Hercules pulling Slipshod in his barrow... :eek:

 

Mr Sworld

Electrical Technician
Joined
Mar 21, 2008
Messages
1,152
Reaction score
0
stupid question time.WTF is the difference?

in a normal domestic does a C and a B really make that much difference?

are you pushing the Zs that close?

I know the characteristics are different, but for a normal joe it should be fine, should it not.?
I was wondering that as well. As I also have just found out that Wylex only do c-type rcbo's.

Would you think it could be caught on a I&T? Would LABC be that fussy?

 

SPECIAL LOCATION

Trailer Boy - Electrician.
Joined
Mar 28, 2008
Messages
13,633
Reaction score
317
I was wondering that as well. As I also have just found out that Wylex only do c-type rcbo's.Would you think it could be caught on a I&T? Would LABC be that fussy?
'Wylex' - 'Volex' - 'Crabtree' all part of same group "Electrium"...

probably all made the same RCBO factory in China...

then housed & badged up accordingly?? ?:| ]:) ] :)

 
Joined
Feb 27, 2008
Messages
11,030
Reaction score
0
stupid question time.WTF is the difference?

in a normal domestic does a C and a B really make that much difference?

are you pushing the Zs that close?

I know the characteristics are different, but for a normal joe it should be fine, should it not.?
Hello steptoe,

I would not agree with this. The zs of c type rcbo as you no is half that of a b type so .60 ohms would be hard to achieve at the end of a long ring main circuit c types are for commercial not domestic. What do you think.

batty

 

kme

Fridge Keyholder™
Joined
Mar 7, 2008
Messages
9,987
Reaction score
0
Location
In the office again.
Hello steptoe,I would not agree with this. The zs of c type rcbo as you no is half that of a b type so .60 ohms would be hard to achieve at the end of a long ring main circuit c types are for commercial not domestic. What do you think.

batty
I`ve now done 3 domestic properties, with wylex boards, filled with C curve RCBO`s. The Zs hasn`t been an issue on any of them; and TBH I don`t expect it to be - at the moment.

To cover myself, I`ve been testing the circuits BEFORE I start the job; so that I can decide whose make to go with. If I DID have a cct which couldn`t take it, I`d have to go with another maker. It`s really not that big an issue.

Alternatively, I have dropped ring circuits (other than kitchen / utility) to a 20A before now.

IMHO