I understand that for a TN system it is 0.4 max disconnection time.
If for a distribution circuit you are allowed 5s max disconnection time, does that mean if you have a garage consumer unit on a MCB of the house consumer unit does that make the circuit a distribution circuit serving the garage and therefore the disconnection time is 5s ? Or have I got that wrong ?
Yes, and you should state that as the maximum discon. time on the cirucit schedule.
Of course, makes little difference in practice, with 60898 B or C, if you are within the tabulated Zs then it'll be going out in less than 0.1s anyway, now a 400A feeder to the far end of a factory on BS88 fuses, that may well take the full 5s
You are thinking along the right lines...
(And once again its another good question, where you put your understanding and thoughts as to what & why you think the answer is how you explained)
But if you re-read section 411 especially 411.3.2.3  and 411.3.2.2,
What conclusions do you come to about final circuits, on a TN system,  supplying fixed equipment,  that have no socket outlets and exceed 32A?
It doesn't actually state ALL TN circuits require a 0.4s disconnection time.
Guinness