It's surprising how often you see it after a tee at the meterprobably something to do with the regs stating its to be on the consumer side of the meter. it should also be before that tee
its also not there to earth the house...
As most service pipes are plastic these days and those that aren't are getting gradually replaced they don't provide any continuity to earth at allCould someone please explain why my earthing is to the house side of the gas meter rather than the incoming pipe? I would have thought that a more reliable earthing would be from the gas mains pipe.
Could someone please explain why my earthing is to the house side of the gas meter rather than the incoming pipe? I would have thought that a more reliable earthing would be from the gas mains pipe.
Water pipe are prohibited as a means of earthing for an electrical installation.
CorrectUnless you have a private supply IIRC
It's usually the case that the boiler fitter has added a new pipe for the new boiler and not bothered to move the bond although I have been to an installation where the bond was moved on the pipe to the wrong side of the new tee so the tee could be installedPossible the Tee was put in after the bond, but should have been moved up before tee at the time
in reality, bugger all if soldered, which I think all gas pipes are.I know that it is a regulation, but given the T is copper, what difference does it make?
I know that it is a regulation, but given the T is copper, what difference does it make?
Incoming gas main should have a main bonding conductor within 600mm of the meter outlet (gs regs)It's surprising how often you see it after a tee at the meter
Did an EICR recently and the smart meter monkey had left a warning notice regarding the position of the earth bond on the gas
if not accessible ie customer has expensive flooring you wouldn't want to disturb, and there is no other suitable access, you can bond elsewhere. 600mm is the recommendation, but not set in stone. You need to test that a suitable earth path is still achieved back to the main incoming point, not hard as there is far more copper in a gas pipe than a 10mm bond cable, and it is advisable to note location of bond on the board. NB this is not acceptable on a new build, when there is no excuse for not bonding at the incoming point, but can be done for upgrading an old bond, such as when changing a board.Incoming gas main should have a main bonding conductor within 600mm of the meter outlet (gs regs)
If the incoming gas main is plastic it doesn't need bonding so there is no "should have" about itIncoming gas main should have a main bonding conductor within 600mm of the meter outlet (gs regs)
Incoming gas main should have a main bonding conductor within 600mm of the meter outlet (gs regs)
Gas regs are law 7671 is guidanceBS 7671 trumps Gas Regs
Since when did plumbers understand electrics?Gas regs are law 7671 is guidance
Gas regs are law 7671 is guidance