I did a periodic last week, and gave a code 1 on an earth clamp on the earth sheaf of a tns supply, (wound up tight it was).
Under regs(as we all know) a bS951 clamp should not be used-Reg 512.1.5
The customer was less than happy as other sparx have never mentioned it.
I informed he she would need to get EDF out .
Had a phone call today from the EDF electrician. telling me the ze is fine so no worries. I said what about the clamp. He just said "nah its ok". and is happy to give cert to say so.
My ass covered.
Opinions anyone?
what would you do?, would you have code 1 it?