Been asked to give a second opinion on an eicr report done by an Niceic company.
Now I know Eicrs are down to the person carrying out the inspection and I'm not wanting to reopen the can of worms about Napits Codebreaker book.
right hopefully that will keep this on track
So tns system 25mm tails 16mm earth and 10mm main bond according to page 2. All good there.
But page 3 3.6,3.7,3.8 C2 as no main bonds according to the description. Hmmmm ok. Maybe standard template used and copied and pasted. Not a good start buy hey
C3 as enclosure not metal so not fire rated. I agree C3 but I thought they were fire rated just not as good ??
4.10 presence of rcd 6 monthly test notice tick
4.18, 4.19 C2 no rcd protection
5.8 C2 no cpc on lighting circuit with metal lights
5.12.1, 5.12.2 C2 no rcds
5.12.3, .4 & .5 all ticked so they must have invisible rcds
6.1 C2 no rcd.
OK so a few issues, but nothing I haven't seen before.
But they have also made a C2 observation as follows.......
"Alliminium conductors throughout rewire recommended"
Now according to the certificate installation is 10years old. According to a quick websearch property was built 1967-1975.
So yes there could be aluminium conductors, but is this a C2 ? Would you rewire just because cables are not copper ??
I'm going to the property tomorrow to give it a quick scope out. Ir readings ok on all but 2 circuits. Downstairs lights l-e 0.14 l-n 0.17 and socket circuit l-e 2.57 but >200 for l-n and n-e.
Oh and the company can do the rewire this weekend in a day with a team of 5. But no plastering and apparently they don't make a mess.
So what's peoples opinions ?
I don't want to post the full report as I don't want to have to edit it to remove names and logos.
I've never had someone say rewire because of Ali conductors. So am very interested in others opinions.
Right I'm off for an ice cream, a cool cider and to sit in a cold bath.
Now I know Eicrs are down to the person carrying out the inspection and I'm not wanting to reopen the can of worms about Napits Codebreaker book.
right hopefully that will keep this on track
So tns system 25mm tails 16mm earth and 10mm main bond according to page 2. All good there.
But page 3 3.6,3.7,3.8 C2 as no main bonds according to the description. Hmmmm ok. Maybe standard template used and copied and pasted. Not a good start buy hey
C3 as enclosure not metal so not fire rated. I agree C3 but I thought they were fire rated just not as good ??
4.10 presence of rcd 6 monthly test notice tick
4.18, 4.19 C2 no rcd protection
5.8 C2 no cpc on lighting circuit with metal lights
5.12.1, 5.12.2 C2 no rcds
5.12.3, .4 & .5 all ticked so they must have invisible rcds
6.1 C2 no rcd.
OK so a few issues, but nothing I haven't seen before.
But they have also made a C2 observation as follows.......
"Alliminium conductors throughout rewire recommended"
Now according to the certificate installation is 10years old. According to a quick websearch property was built 1967-1975.
So yes there could be aluminium conductors, but is this a C2 ? Would you rewire just because cables are not copper ??
I'm going to the property tomorrow to give it a quick scope out. Ir readings ok on all but 2 circuits. Downstairs lights l-e 0.14 l-n 0.17 and socket circuit l-e 2.57 but >200 for l-n and n-e.
Oh and the company can do the rewire this weekend in a day with a team of 5. But no plastering and apparently they don't make a mess.
So what's peoples opinions ?
I don't want to post the full report as I don't want to have to edit it to remove names and logos.
I've never had someone say rewire because of Ali conductors. So am very interested in others opinions.
Right I'm off for an ice cream, a cool cider and to sit in a cold bath.