I haven't bought the radiator yet, I was just checking in advance.What do the instructions say?
Depending on size, its own radial may be required and probably will be suggested by the instructions.
I'll look into it a bit further then. I haven't decided on the type of radiator yet, I was just wanting to see what the normal procedure is first.As Ian says manufactures instructions is the first place to check, power rating would be a key factor. Have you tried looking at manufactures website, many have technical specifications available.Doc H.
fixed loads of over 2KW should ideally have their own dedicated feedHi guys, I haven't installed an electric radiator before and I was just wondering - Is it ok to feed it from a socket circuit using 2.5mm cable via a fused spur?
How so?That only applies to cooking appliances.
Yes, manufacturers instructions over rule every time, however the "2kW rule" is only applicable to cooking appliances.How so?Instructions supplied have to be followed so if they require a dedicated radial then thats what it needs.
How can it be ok to run it on a radial circuit but not on a ring circuit?At the back of BS7671 where it shows a ring circuit, it says something like - space heaters should preferably not be run of the ring that is protected by 30/32amp fuse/mcb.Running it of a radial should be ok but then you looking at possible overloading.
I would try and run a separate circuit.
I think you missed the point. Which is, that it would be on its own dedicated circuit, thus the load is fixed. Unlike a ring where the load is extremely variable.How can it be ok to run it on a radial circuit but not on a ring circuit?
come on now mate do they or dont theyYes, manufacturers instructions over rule every time, however the "2kW rule" is only applicable to cooking appliances.
And where in that thread did i say they didnt?come on now mate do they or dont theyhttp://www.talk.electricianforum.co.uk/showthread.php?t=11548
I though you meant on a radial socket circuit. My apologies! :BlushingI think you missed the point. Which is, that it would be on its own dedicated circuit, thus the load is fixed. Unlike a ring where the load is extremely variable.
your post 8 and 14 mateAnd where in that thread did i say they didnt?