I get what you mean its gonna be a tight squeeze in those volex sockets with 6mm but what other options do i have 2.5mm can't handle 40a even when doubled
Are you saying you want the socket circuit to be rated at 40amp ?
pme & TT sorry im terrible with abbreviations can you recommend somewhere where i can read about all the abbreviations
(from TLC website)
5.6.1 - What is protective multiple earthing?
If a continuous metallic earth conductor exists from the star point of the supply transformer to the earthing terminal of the installation, it will run throughout in parallel with the installation neutral, which will be at the same potential. It therefore seems logical that one of these conductors should be removed, with that remaining acting as a combined protective and neutral conductor (PEN). When this is done, we have a TN-C-S installation {5.2.4}. The combined earth and neutral system will apply only to the supply, and not to the installation.
Because of possible dangers with the system which will be explained in the following sub-sections, PME can be installed by the Electricity Supply Company only after the supply system and the installations it feeds have complied with certain requirements. These special needs will be outlined in {5.6.4}.
The great virtue of the PME system is that neutral is bonded to earth so that a phase to earth fault is automatically a phase to neutral fault. The earth-fault loop impedance will then be low, resulting in a high value of fault current which will operate the protective device quickly. It must be stressed that the neutral and earth conductors are kept quite separate within the installation: the main earthing terminal is bonded to the incoming combined earth and neutral conductor by the Electricity Supply Company. The difficulty of ensuring that bonding requirements are met on construction sites means that PME supplies must not be used. Electricity Supply Regulations forbid the use of PME supplies to feed caravans and caravan sites.
but just out of curiosity why can i not go back to the house CU
Well you can if you wish (called exporting pme) but if there are any extraneous conductive parts (such as metal frame / piped services) you run into hassel with bonding
So my personal prefrence is to TT outbuildings, but as said others do export PME.
Oh TT means
Terra Terra (earth earth) and relates to the incomming supply earthing arrangements, so TT is saying the earthing is the earth (soil) hence you require a rod in the deck to connect the main earthing conductor to.
Hope that explains it a little for you.
you say i shouldn't run 16mm cable from the fuse can you explain a little more why not to, as the cables going into a 63a rcd fuse anyway
Yes the 16mm will be rated at 63a (taking other factors into account) but as you say it will be going from the henly blocks in to the 63amp rcd.....soooooo the only over current protective device protecting the 16mm (63amp) tails will be the big main suppliers fuse rated at (I hazzard a guess) at
100amp, so under fault conditions the tails will probably ignite before the fuse blows.
The Godfather ill search for some 10mm swa cable and see how much that can be bought for then it would be cheaper to use what i have now 2x25m 16mm tails
Put the 16mm tails on ebay or here on T.E.F then use the procceds to buy the 10mm (2core 10mm & use the armour as cpc... it'll be slightly cheaper)