Fire alarm mains supply

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.
Joined
Feb 14, 2008
Messages
7,470
Reaction score
21
Location
Cloud Cuckoo Land
The supply mains cable must be wired in a fireproof cable. An unswitched spur is not good enough for local isolation. You should fit a grid arrangement with a keyswitch and fuse to get the double pole isolation. I expect this will eventually filter through to all items that have an unswitched spur Even i got it wrong untill a couple of years ago.

 
Yes, it should also have its own Isolator with mcb, ideally lockable or fish key type and not spured off from a socket or light supply, it should be labled "Fire Alarm Supply do not switch off", on a red notice board or Fade Free Durable sticker.

 
Yes, it should also have its own Isolator with mcb, ideally lockable or fish key type and not spured off from a socket or light supply, it should be labled "Fire Alarm Supply do not switch off", on a red notice board.
I recently quizzed the NIC about this. I always used to fit a separate red switch fuse labeled 'Fire alarm, do not switch off'. I can find no reference to the separate isolator in either BS7671 or BS5839.

 
BS 5839 25.2 c to f)

"To facilitate local isolation during maintenance, suitable means should be provided for double pole isolation of the low voltage supply circuit that serves the power supply and control equipment."

 