Not sure about this one so looking for a bit of help.
I've got my Elecsa assessment coming up in a few weeks and was going to do a CU change at my place.
Thought I'd better test out the wiring first and came across a 1.5 mm going to my fridge socket. It's on it's own 6 amp MCB and there's only the one socket on it. It is labelled as water heater, we moved the boiler into the loft when we moved in and stuck the fridge in its place.
I think this is a bit unusual hence the question, but I can't see any reason why there is anything wrong, MCB rating will protect cable and it's not a long run, probably about 5 metres.
Any thoughts would be appreciated
Thanks