G59 Protection Relay

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

adammid

Member
Joined
Jun 26, 2012
Messages
238
Reaction score
0
Can anyone inform me as to what a G59 protection relay is used for and does anyone have an indication of the cost. Many thanks in advance

 
It is a loss of mains protection relay.

Cost?  Shade less than a wedge.

(£1000).

It is necesary when the source of

energy produces a supply that is

in parallel (synched on) to the grid.

It is not necessary in domestic solar

because this is single phase.

 
Last edited by a moderator:
Many thanks Tech. For clarification they are only required on three phase systems? What if the PV system is single phase, however forms part of a three phase supply ie the main incomer is three phase??

 
As I see it, it would be unwise to connect a single phase

PV array to a three phase system. There would be several

issues, not the least of these would be balancing.

Someone might have other ideas but any source of energy

producing a three phase energy source needs one of these

as protection should mains power be lost for whatever

reason.

The name of the device is from a guidance note on the

connection of energy sources to the grid of less than

50 kW or aggregate of 50kW.

 
You can get smallish 3 phase inverters starting at 5kW. if you have 3 phase supply you can install 12kW without talking to DNO, though if you ask nicely they may let you have a bigger system assuming you have the roof space. Some popel also fit 3 small inverters, 1 per phase, but I'm not convinced that they would balance properly.

 