Replaced an old Wylex fuseboard (BS3036 fuses) the other day.
TNCS supply with Ze 0.14ohm.
I was expecting fast rcd trip times on x1 and x5, but x1 are surprisingly high. Tried 0 and 180.
Examples of some of the readings:
Sockets (ring) Zs 0.28ohm, RCD 43ms@x1 and 22ms@x5.
Sockets (radial) Zs 0.32ohm, RCD 53ms@x1 and 22ms@x5.
Upstairs Lights (radial) Zs 0.69ohm, RCD 39ms@x1 and 8.5ms@x5.
Used a Crabtree Starbreaker dual RCD board with 30mA RCDs.
Tried swapping circuits between the RCDs but got similar readings.
Tested with Fluke 1653 MFT.
BTW: the upstairs and downstairs lights seem to be sharing a neutral, so they've had to go on the same RCD. Insulation tests all gave 500Megohm.
Very quirky results.
Anyone ever had a similar problem?
Not really sure what to do. I've told customer that his RCD disconnection times are outside of BS7671 and I'll be stating that on the EIC. Trouble is I haven't sussed out exactly why.
TNCS supply with Ze 0.14ohm.
I was expecting fast rcd trip times on x1 and x5, but x1 are surprisingly high. Tried 0 and 180.
Examples of some of the readings:
Sockets (ring) Zs 0.28ohm, RCD 43ms@x1 and 22ms@x5.
Sockets (radial) Zs 0.32ohm, RCD 53ms@x1 and 22ms@x5.
Upstairs Lights (radial) Zs 0.69ohm, RCD 39ms@x1 and 8.5ms@x5.
Used a Crabtree Starbreaker dual RCD board with 30mA RCDs.
Tried swapping circuits between the RCDs but got similar readings.
Tested with Fluke 1653 MFT.
BTW: the upstairs and downstairs lights seem to be sharing a neutral, so they've had to go on the same RCD. Insulation tests all gave 500Megohm.
Very quirky results.
Anyone ever had a similar problem?
Not really sure what to do. I've told customer that his RCD disconnection times are outside of BS7671 and I'll be stating that on the EIC. Trouble is I haven't sussed out exactly why.