High Ze Tncs 0.70 Ohms
Dal Roberts
Nov 14, 2014
83
Essex
High Ze, on TNCS 0.70 ohms - In country area (possibly far from transformer) , getting Zs on 32a ring, 1.60, 1.66 . 1.67ohms - Would anyone suggest I convert to radial and put them on 20a 60898s  to fall within Maz Zs which is 1.74 ohms
25mm tails and 16mm PME , can't do much more , any suggestions would be appreciated
Amendment 3 , with temperature factor taken into account
1.08 max now also on 32 b 60898s
well you could always get DNO to fix it since its way above the max allowable under ESQCR & 7671...
Cant say about the armour slice as I don't have one, but have never had a problem with a good old fashioned hacksaw tbh, theyd probably be ok if you had loads of SWA ends to make off.
I have had a Jokari though, and personally found it to be an utter waste of time. That's not say someone a little more dextrous than me might be the same tho
thanks for all your input D.N.O call tomorrow
C.K Armour slice , anyone got one? I'm thinking about it if there any good reviews ,
https://www.youtube.com/embed/zforoJL4BiU?feature=oembed
CK Armor Slice is bloody brilliant blades last for ages its quick and accurate. Worked well on everything from a 1.5 3c upto a 25 4c for myself and can do bigger sizes. Been used well over 100 times now love it, was quite skeptical after how carp the kewtech thing was but the CK version is in a whole league of its own, well worth every penny.
Another great piece of kit from CK.