B bharlow New member Joined Mar 20, 2014 Messages 1 Reaction score 0 Mar 20, 2014 #1 I am buying a new built-in hob to replace an old one. The maximum power rating of the new hob is 7.1kw. Will this fit/work on the existing 32amp spur once the old hob is removed (nothing else will be on that spur)?
I am buying a new built-in hob to replace an old one. The maximum power rating of the new hob is 7.1kw. Will this fit/work on the existing 32amp spur once the old hob is removed (nothing else will be on that spur)?
ProDave Twatt ™ Supporting Member Joined Nov 28, 2009 Messages 14,841 Reaction score 1,026 Mar 20, 2014 #2 7.1KW is 30.8 amps so you will be fine.
m4tty Scaredy cat™ Supporting Member Joined Feb 5, 2009 Messages 5,612 Reaction score 1 Mar 20, 2014 #3 ^^ what he says ^^ The cooker has got its own circuit and is not spurred of something else tho