{The first 18 posts in this thread have been removed from another thread due to the apparent hi-jacking of someone else's question, (A new members first post!) and taking it even more off topic than it had already drifted.
Original posts can be seen here.
http://www.talk.electricianforum.co.uk/inspection-testing/17503-insulation-resistance-testing-socket-outlet.html#post236017
We aim to keep the forum open for all manner of constructive debate, (even the wording of BS7671 and its related publications), but if you wish to argue these topics, please have respect for the original thread starter's question. They do not want to keep checking back for more helpful information of their thread topic only to find some member calling other members smart a***s or T*****s This is not acceptable or within the forums T&C's which can be read here.
vBulletin FAQ
Thank you
Doc H.
}
======================================================================
======================================================================
Moved posts commence here:
=======================================================================
=======================================================================
Even testing L&N connected together to Earth, I would still want all loads removed - in particular, anything plugged in, any transformers, dimmers etc.
The reason I say this is that, although we know that the chances of equipment damage is minimal when testing 'live' conductors together to earth - when, by pure coincidence, the customers computer no longer works after your visit, they're going to say "It was fine before you plugged your tester in to my socket"!!
So, be wary, not such a simple test.
GN3 states: PG 38
Original posts can be seen here.
http://www.talk.electricianforum.co.uk/inspection-testing/17503-insulation-resistance-testing-socket-outlet.html#post236017
We aim to keep the forum open for all manner of constructive debate, (even the wording of BS7671 and its related publications), but if you wish to argue these topics, please have respect for the original thread starter's question. They do not want to keep checking back for more helpful information of their thread topic only to find some member calling other members smart a***s or T*****s This is not acceptable or within the forums T&C's which can be read here.
vBulletin FAQ
Thank you
Doc H.
}
======================================================================
======================================================================
Moved posts commence here:
=======================================================================
=======================================================================
I wouldn't call testing IR at a socket outlet a 'quick and easy test'.anything else i should keep in mind about this,
Even testing L&N connected together to Earth, I would still want all loads removed - in particular, anything plugged in, any transformers, dimmers etc.
The reason I say this is that, although we know that the chances of equipment damage is minimal when testing 'live' conductors together to earth - when, by pure coincidence, the customers computer no longer works after your visit, they're going to say "It was fine before you plugged your tester in to my socket"!!
So, be wary, not such a simple test.
IR testing is meant to be done on the whole installation (or section of installation e.g. at each DB) - it's not meant to be done circuit by circuit...........the figure that we need to comply with is meant for the 'whole' installation.....if the IR test result for the whole install is within the regs, then the IR of any single cct must compy.
GN3 states: PG 38
Simple installations that contain no distribution circuits should be tested as a whole.