is an rcd a primary device for protection?

Talk Electrician Forum

Help Support Talk Electrician Forum:

This site may earn a commission from merchant affiliate links, including eBay, Amazon, and others.

Lee321

Distinguished Member
Joined
Sep 8, 2008
Messages
2,141
Reaction score
0
a property can have no earthing (very old) and rcd will provide protection against direct and indirect contact?

 
a property can have no earthing (very old) and rcd will provide protection against direct and indirect contact?
No. RCD's are only classed as additional protection (411.3.3).

While lighting circuits without earths can be allowed (with provisions attached) a property with no earths on all other circuits is a re-wire situation. :)

 
No. RCD's are only classed as additional protection (411.3.3).While lighting circuits without earths can be allowed (with provisions attached) a property with no earths on all other circuits is a re-wire situation. :)
do u mean as long as the lighting circuit has no metal fittings or switches

 
No. RCD's are only classed as additional protection (411.3.3).While lighting circuits without earths can be allowed (with provisions attached) a property with no earths on all other circuits is a re-wire situation. :)
The Godfather agrees.

Don

 
I'm glad. I can sleep easy tonight! :^O