Hi Guys
installed new circuit for shower (7.8kW 230v/8.5kW 240v) in 6mm today. I also installed a mem alb321 rcbo. Test results were r1+r2 0.07, I/R 500+ Zs 39.68. RCBO test button works but fails to trip during test. I removed the load & tried RCD test again but no trip.
Installation is a TT system with 100a 100mA RCD main switch (Ze 36 ohms). 6mm main earthing conductor, 10mm bonds to gas & water.
During RCD tests the 100mA tripped at 17.6ms at x5.
Out of curiosity i then tested the rcbo for the hob & socket circuits. Both failed to trip during test, yet the 100mA tripped during x5.
I even turned off all circuits except circuit being tested & same results, none of the 3 rcbo's will trip whether tested at the rcbo or at hob/shower or sockets.
Any help appreciated
Thanks