Not in the regs..Is there a maxium meter tails length as I have a pizza shop that requires the old consumer unit connecting up with the new supply that is seven meters away at the front of the shop.
But in reality, that is the norm, is it not?Locally 3m is max length, so imagine my surprise when I looked at a new flat conversion with meter tails running to each flat from the underground parking area, straight from the meters. The building is 3 storeys high .
so would you give this a separate cert and another for the CU?Not in the regs..But DNO will often specify max permissible lengths without additional isolator & overload protection.
e.g. page 17 OSG paragraph 2.2.3 Meter Tails.
I think 5m is a length at which it is a big no-no for direct connection to meter without isolation.
If you put a isolator & overload protection it effectively becomes a distribution circuit. such that the DNO's cut out is only protecting a short run to your Isolator.
I have done a 16m run from Cut out to Cu,
I used 25mm SWA via an 80A cut out switch.
Sounds a bit overkill to me Craig.so would you give this a separate cert and another for the CU?
If you look at certs there is a bit about not being directly connected to supply, and top line of NIC certs has black box for distribution circuits.so would you give this a separate cert and another for the CU?
i have had an email back from NEDL saying "Thank you for your e-mail, you will need to speak to your own electrician this is something that we don
i have had an email back from NEDL saying "Thank you for your e-mail, you will need to speak to your own electrician this is something that we don