MK Sentry - Advice Needed, Please?

Help Support Talk Electrician Forum:

welshwizard

Honorary Life Member
Joined
Feb 12, 2008
Messages
1,657
Reaction score
-1
Hi Guys,

Received an E-mail asking to buy my 80A 30ma RCCB.

The Gentleman stated that the spark had fitted a 300ma in error.

Gentleman & I agreed a price, Item sent - Item Received.

Is there any reason why this chap can't use the RCCB? He says his Board was changed to an MK Sentry in July 1994.

Many Thanks,

Jamie.

 

steptoe

of course Im wrong, ask my wife™
Joined
Feb 13, 2008
Messages
24,386
Reaction score
152
Location
Gtr Manchester
for a standard install the 300mA one would just be wasting space and would prob never trip in any decent length of time.

is it a farm or something? then that would make sense.

as for yours, 2kA is actually pretty low breaking capacity, might not be suitable depending on his supply, ie. PME, cable sheath, TT etc, would need a PSCC to be sure.

 

welshwizard

Honorary Life Member
Joined
Feb 12, 2008
Messages
1,657
Reaction score
-1
Hi Steptoe,

It's a house, Mate. I have E-mailed to ask his supply type.

here's two more pics that he has emailed me.

pic2-1.jpg


*** CLICK HERE TO ENLARGE THE ABOVE PICTURE ***

pic1-1.jpg


*** CLICK HERE TO ENLARGE THE ABOVE PICTURE ***

.

 

extension15

Distinguished Member
Joined
Feb 13, 2008
Messages
1,658
Reaction score
0
Not that sure WW, but 2KA does seem very low, by todays standards..

I'll bid you goodnight..

ps 99 members, well done...

:D

 

welshwizard

Honorary Life Member
Joined
Feb 12, 2008
Messages
1,657
Reaction score
-1
Not that sure WW, but 2KA does seem very low, by todays standards..

Ok EXT - Thanks for looking.

I'll bid you goodnight..

Goodnight to you, Sir.

ps 99 members, well done...

Indeed Mate. Going very well, considering it was opened on the 13th of February. I wonder who 100th person to register is going to be.

 

the doctor

Part P Doctor ™
Joined
Mar 1, 2008
Messages
580
Reaction score
0
hi

the 300mA rcd is a waste of time on this jobbie because it only takes around 50-80mA to kill you so.....

up to 30mA shock protection (supplementary protection from direct contact)

above 30mA fire protection only ( indirect protection only)

thats why there are TWO rcd boxes on an inspection schedule-if you fit a 30 model you can tick BOTH boxes- direct AND indirect contact...

with a 300 you can only tick the indirect protection box....

 

welshwizard

Honorary Life Member
Joined
Feb 12, 2008
Messages
1,657
Reaction score
-1
Hi Doc, The Gentleman's Spark put in the 300ma in error.

I sold the RRCB to him. (I knew nothing of this situation at the time).

I have since, sourced an 80 A MK LN 5780s 30ma for the Gentleman.

And posted it off - this morning.

 

the doctor

Part P Doctor ™
Joined
Mar 1, 2008
Messages
580
Reaction score
0
hi

thats good!

never been a fan of those mk boards, it seems they never look great inside when connected...

 

steptoe

of course Im wrong, ask my wife™
Joined
Feb 13, 2008
Messages
24,386
Reaction score
152
Location
Gtr Manchester
not been a fan of anything MK for a long time TBH, but.....

my missus just seen some MK sockets and she likes them so guess what.?

yep, Im going for the quiet life....

anyhoo, glad you got the RCCB sorted.

 