As far as I know ( and is know very little) there is no requirement to use ring crimps, although it is good practice toGas bonding conductor incorrectly terminated with no ring crimps, and no "do not remove" tag.
"Unsatisfactory".
i would not consider any of those to be C1. C2 at worstThanks for that, I'll take a look.
115 observations in total - lots of C2's and a few C3's, with some FI's and Notes
4xC1's:
- 5.13 provision of fire barriers (section 527)
- 5.14 band II cables segragated / separated from band I cables (528.1)
- 5.15 cables segregated / separated from comms cabling (528.2)
- 5.16 cables ... from non-electrical services (528.3)
no other comments at all?
when you get to 5 posts you should be able to load photo's etc
Ah, page 9 has a "general condition of the installation", and says
"Aging installation with a large number of non-conformities. No 30mA RCD protection installed to required circuits".