Will start by apologising if this is long winded. I subcontract as a Mate & don't normally do my own work, yet have been asked to look at tidying up a supply to an outbuilding. Would like some clarification on what I've done & if I'm right? Or where I've gone wrong...
The outbuilding is currently used as a Bicycle Frame Spray Booth & Garage. He does Braze the odd Bicycle Frame in here too with Gas Flame Torch. From the House he has what looks to be 2.5mm SWA wired into some kind of plug in adaptor to a Socket Outlet. Runs 50-60m to the RCD Board in the Outbuilding. Causing nuisance tripping I believe or could be taking out the RCD on the Board in the House.
At the House end:
Main CU is a Push Fuse Type, no RCD. Incoming Supply Fuse marked up as 60A
Split off this is a MEM Fuse running to a Sub board in the Kitchen Extension, 16th Ed all ways have 30mA RCD Protection.
All Tails at Main CU & Henley Blocks look to be 25mm & 16mm Earthing Conductor.
There are spare ways on the Sub Board but I have no means of splitting the supply there to give me Sole RCD Protection for the outbuilding without affecting the circuits in the extension.
At the Outbuilding:
2.2KW Air Compressor
1.5KW Fan Extractor (In the Booth)
2.5KW Heater (In the Booth)
6x 70W Fluorescent Fittings
1x 500W Halogen Security light, used as a second light in the Booth.
4x Sockets
Maths:
Max Demand (Ib) at the Outbuilding using diversity on the lighting only = 50.56A
I've used a 20A Radial for the sockets, so 30.56A from everything else + 20A
In = 63A (even though it's just over 50A)
It = 63A (External run, but no Ambient Factor applied)
VD = 13V (Over 5%, or should I use 3% as I have lighting in the outbuilding?)
Cable Selection SWA Clipped Direct along a Concrete Fence Support. Now based on 5% both 10 & 16mm too small for VD.
Any way of reducing the Max Demand at the Outbuilding? I know the Fan & Compressor will be on together along with the lights. I'm assuming the heater is used afterwards almost as a baking process & sockets, well maybe he'll now plug in a radio or phone charger, or small hand tool - Grinder/Drill?
Also, it got pointed out that I might need to be aware of the conditions of switchgear & ventilation due to the spray booth. He has a Main CU & Sockets etc already in there (outside of the booth) & uses a Gas brazing torch in the same environment, so if explosive/flammable environment due to paint he's using, I'd have thought there'd already be an issue?
Any pointers? I did work out R1+R2/ZS/Fault etc but then realised I was over on the VD...
The outbuilding is currently used as a Bicycle Frame Spray Booth & Garage. He does Braze the odd Bicycle Frame in here too with Gas Flame Torch. From the House he has what looks to be 2.5mm SWA wired into some kind of plug in adaptor to a Socket Outlet. Runs 50-60m to the RCD Board in the Outbuilding. Causing nuisance tripping I believe or could be taking out the RCD on the Board in the House.
At the House end:
Main CU is a Push Fuse Type, no RCD. Incoming Supply Fuse marked up as 60A
Split off this is a MEM Fuse running to a Sub board in the Kitchen Extension, 16th Ed all ways have 30mA RCD Protection.
All Tails at Main CU & Henley Blocks look to be 25mm & 16mm Earthing Conductor.
There are spare ways on the Sub Board but I have no means of splitting the supply there to give me Sole RCD Protection for the outbuilding without affecting the circuits in the extension.
At the Outbuilding:
2.2KW Air Compressor
1.5KW Fan Extractor (In the Booth)
2.5KW Heater (In the Booth)
6x 70W Fluorescent Fittings
1x 500W Halogen Security light, used as a second light in the Booth.
4x Sockets
Maths:
Max Demand (Ib) at the Outbuilding using diversity on the lighting only = 50.56A
I've used a 20A Radial for the sockets, so 30.56A from everything else + 20A
In = 63A (even though it's just over 50A)
It = 63A (External run, but no Ambient Factor applied)
VD = 13V (Over 5%, or should I use 3% as I have lighting in the outbuilding?)
Cable Selection SWA Clipped Direct along a Concrete Fence Support. Now based on 5% both 10 & 16mm too small for VD.
Any way of reducing the Max Demand at the Outbuilding? I know the Fan & Compressor will be on together along with the lights. I'm assuming the heater is used afterwards almost as a baking process & sockets, well maybe he'll now plug in a radio or phone charger, or small hand tool - Grinder/Drill?
Also, it got pointed out that I might need to be aware of the conditions of switchgear & ventilation due to the spray booth. He has a Main CU & Sockets etc already in there (outside of the booth) & uses a Gas brazing torch in the same environment, so if explosive/flammable environment due to paint he's using, I'd have thought there'd already be an issue?
Any pointers? I did work out R1+R2/ZS/Fault etc but then realised I was over on the VD...