I have installed a outside socket, wired it the apropiate cable using 13amp plug too plug into a indoor socket all tested to make sure wired correctly.Soon as I turn any appliance on outside it trips the RCD in the consumer box. Any ideas what is causing this please
at a guess...
Either the appliance is faulty,
or you've wired it wrong,
or the cable is damaged...
N & E shorted..
N & E crossed..
etc..
Correct dead testing prior to energising would prevent these sort of problems..
Have you done any testing of the circuit prior to adding it or tested the new socket in any way other than plugging something in? What was the result?
Is it a case of uprating the RCD from 80A- 30ma to 100A-30ma
The 80A (Amps) is the amount of current that the RCD can safely switch off when it operates, so changing it to one that can switch off 100A (Amps) would be of no use what so ever, since the problem will still be there.
The fault that is causing the problem needs to be found, this is often best carried out by using the correct test equipment, which is what Sharpend said.
No, all this shows is that you have no understanding of what an RCD actual does..
It is there to detect electrical leakage current.. i.e. electricity flowing to earth..
Both of the RCD's you describe will detect 30ma leakage..
which actually means..
they both must not trip at 15ma..
they both must trip at 30ma..
and they both could trip anywhere from 16ma to 29ma as well.
You have got a fault with your wiring..
which would have been detected had you done correct 'dead' continuity, polarity and insulation resistance tests,
prior to energising your alteration..
If you say the appliance works ok in another socket then that still leaves some other items from my earlier list you need to check..
Either you've wired it wrong or the cable is damaged...
My guess N & E shorted or N & E crossed..
There's only really 4 options.
Faulty main socket your drawing the power from. Faulty wiring in the plug. Damaged wire or faulty wiring in the outdoor socket.
How to check. Eliminate the main socket by running a extension to another socket not on the same ring main.
Check the plug and socket to make sure it's wired correctly. Of all above is correct Then change cable
Plugged in my socket tester all was ok
It needed more than a socket tester to check it before you made it live. Aside from saying get someone qualified in to check it and fix it I'd suggest you have got your cables mixed up so turn the power off and check they are correctly connected. Most likely the N and E are crossed which your tester wouldnt identify. The equipment you are plugging in can be checked elsewhere to rule that out of the equation
Just out of interest, what is the cable you have used? im assuming 1.5mm flex, or have you used t&e?
Im guessing N & CPC reversed with in the plug or in the socket