Or earthed armouringDepends on the run of the cable in the building - it may have to be RCD'ed to comply with the 17th.Just remember submains can have a disconnection of 5 seconds.
D.
if its PME/TNCSPersonally I would see that as a sub-main to another building and do'nt see the need for the RCD. In the out-building I would probably fit what I call a Garage Unit which is really a 2way consumer unit, RCD as main switch feeding a 6amp and a 16amp MCB s . If using SWA cable would always use a 3 core,using third core as earth.Deke ( Waiting to be shot down )
to quote specs 'thought it was a workshop'................I cook wit Gas (WTF? I hear you ask)....I cook with gas and therefore don't use the cooker point (MCB Side of CU). I have 3 core 6mm SWA going to shed (Approx' 17 metres). I have it terminated into a Two way RCD main switch Garage consumer unit. I have the lighting on 6 A and have changed the 16 A to 32 A because of the number of s/o's that I have added.
well I hope your building at the bottom of the garden hasnt got an exported PME????It is a workshop/shed guys.
Is it painful?I`ve got TNC-S/PME.
Stop tampering with my quotes. I had to double check that I hadn't put that. :^OIs it painful?Do you get discharges from that?
Have you been to see the doc?
IS IT CATCHING?!?!?!?!?!
( The Nackered Car - Syndrome / Poxy Motor Effed)
:^O :^O:^O:^O:^O
quote away bud! ; \to quote specs 'thought it was a workshop'................
its been a major bone of contention EE,Hey Steps I've only been in the trade for 40 years but I must admit that you've thrown me with reference to the Exported earth. If you run a sub-main from one building to another, whats the problem with the earth ? Excuse my ignorance, lets face it there is always something new to learn in this trade.Deke
Somethig I can do................there is another thread on here about it perhaps someone that knows how could link it for you.
the big mamma of an exported earth thread Applaud Smiley:^O:^O:^O:^OSomethig I can do................There's me modest exported earth thread
http://www.talk.electricianforum.co.uk/showthread.php?t=1559
And the big mamma of an exported earth thread with name calling, calculations and everything
http://www.talk.electricianforum.co.uk/showthread.php?t=483&highlight=exporting+earth
:^O :^O:^OSomethig I can do................There's me modest exported earth thread
http://www.talk.electricianforum.co.uk/showthread.php?t=1559
And the big mamma of an exported earth thread with name calling, calculations and everything
http://www.talk.electricianforum.co.uk/showthread.php?t=483&highlight=exporting+earth