T teddyc Junior Member Joined Jul 11, 2011 Messages 3 Reaction score 0 Jul 12, 2011 #1 Hi Testing 1st floor office floor sockets is there a need for them to be RCD protected as it is impossible for them to be used for outside use, what recommendation code should i use. Thanks
Hi Testing 1st floor office floor sockets is there a need for them to be RCD protected as it is impossible for them to be used for outside use, what recommendation code should i use. Thanks
kme Fridge Keyholder™ Supporting Member Joined Mar 7, 2008 Messages 9,984 Reaction score 0 Location In the office again. Jul 12, 2011 #2 A bit more info needed - sorry; and welcome to the forum. 1. Are the sockets going to be used by anyone: a) not employed by the company? B) for any equipment other than the company`s? 2. What is the wiring system? Does the wiring itself require protection? 3. What is the earthing system / EFLI at the outlets? Do you need to provide "additional protection" to comply with disconnection times for the OCPD? 4. Can you apply one of the "get out" clauses for sockets < 20A? Give us that lot, and we`ll talk some more...... KME
A bit more info needed - sorry; and welcome to the forum. 1. Are the sockets going to be used by anyone: a) not employed by the company? B) for any equipment other than the company`s? 2. What is the wiring system? Does the wiring itself require protection? 3. What is the earthing system / EFLI at the outlets? Do you need to provide "additional protection" to comply with disconnection times for the OCPD? 4. Can you apply one of the "get out" clauses for sockets < 20A? Give us that lot, and we`ll talk some more...... KME
matt.leung Well-known member Joined Feb 26, 2009 Messages 1,062 Reaction score 0 Location Bromley, Kent Jul 12, 2011 #3 dont forget, if they where rcd'ed computer leak current over time tripping the circuit. is there any design info for the installation you to read over.
dont forget, if they where rcd'ed computer leak current over time tripping the circuit. is there any design info for the installation you to read over.
T teddyc Junior Member Joined Jul 11, 2011 Messages 3 Reaction score 0 Jul 12, 2011 #4 Don't think anyone outside of company going to use sockets, only there equipment being used. Wiring is in concealed metal floor trunking Earth loop impedance is 0.28
Don't think anyone outside of company going to use sockets, only there equipment being used. Wiring is in concealed metal floor trunking Earth loop impedance is 0.28
Evans Electric TEF LINUX ADMIN™ Supporting Member Joined Sep 15, 2008 Messages 23,507 Reaction score 527 Location Birmingham Jul 12, 2011 #5 As far as I know then, RCD is not required , the words cans and worms come to mind , probably 16th edit. leave it alone .
As far as I know then, RCD is not required , the words cans and worms come to mind , probably 16th edit. leave it alone .
SLIPSHOD & SLAPDASH Gold Member Supporting Member Joined Feb 14, 2008 Messages 7,470 Reaction score 21 Location Cloud Cuckoo Land Jul 12, 2011 #6 I find 99.9% of PIR will have at least a code 4 starter for, 'Wired to an earlier version of the regulations'
I find 99.9% of PIR will have at least a code 4 starter for, 'Wired to an earlier version of the regulations'
matt.leung Well-known member Joined Feb 26, 2009 Messages 1,062 Reaction score 0 Location Bromley, Kent Jul 12, 2011 #7 i was reading an artical today, and it stated that on the new PIR forms, there will be no code 4's anymore.
i was reading an artical today, and it stated that on the new PIR forms, there will be no code 4's anymore.