Hello.
I am planning on rewiring my garage for my assessment with elecsa and am having trouble confirming the correct size with the OSG when in conduit. With a type B 32A cb I can use 2.5 t&e with ref methods A,100,102 & C. AIUI conduit is B. This suggests that t&e should not be used in conduit (I was planing on using 2.5 singles for L&N and 1.5 singles for CPC) but there doesn't appear to be any mention of ref B in any of these tables or any tables for singles.
Does anyone know where (if anywhere) it is stated that 2.5/1.5 singles are ok in conduit for a Final Ring Circuit protected by a 32A type B cb?
I was also planning (until I couldn't find the tables) to use 1.5/1.5 singles for the lighting in conduit too.
Thanks.
Ian.
I am planning on rewiring my garage for my assessment with elecsa and am having trouble confirming the correct size with the OSG when in conduit. With a type B 32A cb I can use 2.5 t&e with ref methods A,100,102 & C. AIUI conduit is B. This suggests that t&e should not be used in conduit (I was planing on using 2.5 singles for L&N and 1.5 singles for CPC) but there doesn't appear to be any mention of ref B in any of these tables or any tables for singles.