What about the neutral?The live is going to be continous throughout its length, unless it is not connected somewhere. As is the earth.When you do a temporary connection between live and earth the circuit MUST be dead.
If not you would hear a little bang and a click.
There are normally only Live and Earth at a light switch that is why the temp connection is needed to test continuity between live and earth.
What's to say that the L and E aren't crossed?the test is done to make sure that it is switching the live cable and not the neutral.
When carrying out the polarity test on a lighting point, with the test being carried out between L and E, how can you tell that L and E aren't wired the wrong way round?Not sure I follow. You mean if the switch was on the cpc (BAD)? Then if the light was wired to line and neutral then the light would never switch off and if it was wired to cpc & neutral then your RCD will probably trip but no light.
Don't forget the Inspection part of Inspection and Testing. Inspection will reveal faults that Testing cannot.When carrying out the polarity test on a lighting point, with the test being carried out between L and E, how can you tell that L and E aren't wired the wrong way round?
Aye, I know that part, but what I can't understand is why between L and E???ES lamps are polarised too. So you need to test from center pin to cpc in rose via loop in CCU (L & E linked) and it should be a complete circuit depending on the switch position.
It is possible to switch a light using the nuetral but it is not allowed for obvious reasons.Aye, I know that part, but what I can't understand is why between L and E???
Because, the reading you obtain, in ohms, is R1+R2 for that light point.Aye, I know that part, but what I can't understand is why between L and E???
Except that insulation resistance is carried out AFTER continuity tests!Your IR test (at the board end) will have already proved there is no cross connection between any of the 3 conductors.