Been called out to a school that's had a flood due to having the lead ripped off the roof.
Replaced loads of panel leds due to water ingress but when testing there is no earth continuity on the cables feeding each driver and pir.
They were fitted in 2019/20 by some company that used wago connectors and no boxes. I know that's a non compliance, but do you need to have a cpc in a cable when all the fittings and accessories are class 2 ?
It's wired in 6242y but the cpcs are just sleeved together often not even in a wago.
The school is worried due to non reg compliance of no earth. I have said in my professional opinion the risk to life of an electric shock hazard is minimal as the fittings are class 2 or low voltage.
Obviously there's alot of fittings to check hence why I'm working Sunday but just want to know others thoughts about the situation.
I've not checked the BBB for regs regarding a cpc requirement yet but if anyone knows anything off the top of their head that might save me some time tonight it would be much appreciated.
Replaced loads of panel leds due to water ingress but when testing there is no earth continuity on the cables feeding each driver and pir.
They were fitted in 2019/20 by some company that used wago connectors and no boxes. I know that's a non compliance, but do you need to have a cpc in a cable when all the fittings and accessories are class 2 ?
It's wired in 6242y but the cpcs are just sleeved together often not even in a wago.
The school is worried due to non reg compliance of no earth. I have said in my professional opinion the risk to life of an electric shock hazard is minimal as the fittings are class 2 or low voltage.
Obviously there's alot of fittings to check hence why I'm working Sunday but just want to know others thoughts about the situation.
I've not checked the BBB for regs regarding a cpc requirement yet but if anyone knows anything off the top of their head that might save me some time tonight it would be much appreciated.