Now some may say 'Dude, you're getting well confused'.No, no, no, no, noooooooooooo!!!!!!NEVER do this. Never.
I am shocked and dismayed that three of you think this is acceptable practice.
but I couldn't possibly comment.
In view of the fact that out in the real world there are numerous Earth Loop Impedance testers that either
1) have no anti-trip facility or
2) only perform anti-trip on certain type of RCD / RCBO...
AND
there are still loads of split load boards with several non RCD protected MCB's
or RCBO slots that could temporary be replaced with an MCB....
Then to disconnect the circuit conductors, Live & Neutral (which are probably off while doing other dead tests)
from an RCD protected MCB or RCBO ....
and temporarily reconnect back onto a NON-RCD protected MCB, (of suitable value)
such that it can be said.... "The RCD or RCBO is bypassed".
This posses less risk or danger.... IMHO than say disconnecting the main earth connection to take a Ze reading.....
Or do you frown upon this practice as well ??? ?:| :|
Possibly to verify maximum ZS values.. say in accordance with the information given in Guidance Note 3 around page 50ish???If you can't measure Zs directly (and why would you want to on a new installation?) then calculate in accordance with Appendix 14.
also not ALL installations are new... some of us actually work on existing installations as well.
These are fairly basic tests that some may expect 'every spark to understand'.
Hope that helps.