I've had 2 calls last week about RCD's tripping after we had those thunder & lightning storms. One of them I went round to look at but couldnt find anything wrong. Any suggestions?

 

norv

Senior Member
Joined
Feb 16, 2008
Messages
127
Reaction score
0
Yeah, felt a bit of a let down leaving her with a tripping RCD.

 

Mr Sworld

Electrical Technician
Joined
Mar 21, 2008
Messages
1,152
Reaction score
0
Is the RCD tripping all the time now after the lightning or just tripped during the storm?

 

The Godfather

Retired
Joined
Mar 24, 2008
Messages
1,302
Reaction score
0
I've had 2 calls last week about RCD's tripping after we had those thunder & lightning storms. One of them I went round to look at but couldnt find anything wrong. Any suggestions?
What tests did you do norv?

Don

 
Joined
Mar 28, 2008
Messages
13,619
Reaction score
296
Not had experience of lightning tripping RCD's myself....

but thats not to say in the right circumstances it couldn't happen!

If you say you have checked the RCD & all is working OK and not over-sensetive....

Then I suppose you would need to know what other possible factors e.g..

Did the incoming supply drop for a short while due to surge on another part o the Grid local to your problems.

is there much external wiring acting as nice long aerials to pick up power surges from the storm?

As steptoe says.. TV amps & boosters are quite common to pop during a storm..

Has one or a similar piece of electronic equipment been zapped by the storm trippin the RCD?

Thats about all I can think of at the moment? :|

 

norv

Senior Member
Joined
Feb 16, 2008
Messages
127
Reaction score
0
Its tripping intermittantly after the storm. She said it was ok before. I unplugged everything in the whole house & did Ze, Zs, IR & tested the RCD from a socket. I thought an appliance had got a zap somehow so unplugged all appliances, turned everything back on & plugged 1 appliance back in at a time. RCD stayed on until I plugged the vacuum in. Unplugged the vaccum & then couldnt reset the RCD. Unplugged everything again, reset RCD & then basically ran round in circles for half a day

 

The Godfather

Retired
Joined
Mar 24, 2008
Messages
1,302
Reaction score
0
Norv, did you ramp test the RCD?

I suspect the RCD may be the problem here.

Don & The Boys

 

Mr Sworld

Electrical Technician
Joined
Mar 21, 2008
Messages
1,152
Reaction score
0
Very odd. Can only suggest ramp testing the rcd and possibly replacing it? ?:|

 

norv

Senior Member
Joined
Feb 16, 2008
Messages
127
Reaction score
0
Good thinking about the TV booster. I'll look into it. Going back on the 5th June so wont be able to do anything till then.

Is a TT setup with the 100ma RCD before the old plug in fuse Wylex CU

I wiggled the Main switch of the CU & the RCD tripped aswell.

 

The Godfather

Retired
Joined
Mar 24, 2008
Messages
1,302
Reaction score
0
In this instance (and probably most), where a lightning strike has taken place, the RCD will often taken the full force of any incoming surge.

Don

 
Joined
Mar 28, 2008
Messages
13,619
Reaction score
296
Its tripping intermittantly after the storm. She said it was ok before.
One word of caution.....

Don't let statements like they said it was alright before an event

make you assume an event was the cause?

It may or may not be relevent... can sometimes just be coincidence! :|

 
Joined
Mar 28, 2008
Messages
13,619
Reaction score
296
Good thinking about the TV booster. I'll look into it. Going back on the 5th June so wont be able to do anything till then.Is a TT setup with the 100ma RCD before the old plug in fuse Wylex CU

I wiggled the Main switch of the CU & the RCD tripped aswell.
One other thought????

How old is the RCD??

is this voltage operated:(

or current operated device?? ?:|

 

norv

Senior Member
Joined
Feb 16, 2008
Messages
127
Reaction score
0
Originally Posted by norv I wiggled the Main switch of the CU & the RCD tripped aswell.

Well it would.
Not up & down, left to right

 

The Godfather

Retired
Joined
Mar 24, 2008
Messages
1,302
Reaction score
0
Not up & down, left to right
That's fine but any 'brief' interruption of the Live or Neutral supply to the RCD (and where a current is flowing of the RCD threshold).

One would resonably expect the RCD to trip.

However the Main switch may be a suspect, but my boys have never seen this.

Don

 

norv

Senior Member
Joined
Feb 16, 2008
Messages
127
Reaction score
0
It was an old setup

The RCD wasnt a Voltage operated device, it was Current operated.

 