Hello everyone,
Am hoping you would be able to advise me here. I am a retired sparks so a bit out of date with latest regs etc so posting in the DIY bit.
I have a split 2 bank Wylex CU with both banks protected by 80A 30mA RCDs. There is a single socket just below the CU wired as a spur from the gnd floor RM. Whenever I plug mr wifi router into this socket it takes out the RCD - sometimes both RCDs. I have tried 2 other routers (one with an external power supply) and the same thing happens. Even if I wire the router power lead directly into one of the circuit breakers it happens. Weirdly, if I plug any of the routers into the wall socket 1 metre away it's fine.
Wylex tech support were stumped but suggested it could be a shared neutral issue - not sure if I agree with that.
I'm thinking it must be something to do with the surge of the transformer being so close to the CU? Thinking along these lines I plugged a 10 metre extension lead into the single socket and the router into the end of that but it still tripped.
In terms of a solution, I could look to getting one of the RCDs replaced with an isolator (being mindful of what circuits should and shouldn't be RCD protected of course) but that isn't really solving the reason of why it's happening.
I'd love to know what's going on here.
Am hoping you would be able to advise me here. I am a retired sparks so a bit out of date with latest regs etc so posting in the DIY bit.
I have a split 2 bank Wylex CU with both banks protected by 80A 30mA RCDs. There is a single socket just below the CU wired as a spur from the gnd floor RM. Whenever I plug mr wifi router into this socket it takes out the RCD - sometimes both RCDs. I have tried 2 other routers (one with an external power supply) and the same thing happens. Even if I wire the router power lead directly into one of the circuit breakers it happens. Weirdly, if I plug any of the routers into the wall socket 1 metre away it's fine.
Wylex tech support were stumped but suggested it could be a shared neutral issue - not sure if I agree with that.
I'm thinking it must be something to do with the surge of the transformer being so close to the CU? Thinking along these lines I plugged a 10 metre extension lead into the single socket and the router into the end of that but it still tripped.
In terms of a solution, I could look to getting one of the RCDs replaced with an isolator (being mindful of what circuits should and shouldn't be RCD protected of course) but that isn't really solving the reason of why it's happening.
I'd love to know what's going on here.